Farmelectrics
before changing db you have to prove that the installation is ok to accept 17th edition boards a landlord has asked me to change 12 in a block of flats now usually i would do full test on boards but bearing in mind the prices are tight not wanting to spend to much time would i get away with just an insulation test between LN together to earth your thoughts please
visual inspection, then IR . test for borrowed neutrals. if you have an earth leakage clamp meter, check if there's any apparent earth leakage. measure Ze. CONFIRM EARTHING AND BONDING. lack of bonding can bite you in the pocket.
The above tests should be enough to change the board and if the IR tests are 8 Meg and above the RCD's will hold no problem at all.
Its the unexpected faults that you have to look for ie no continuity on final rings ccts very high R1 +R2 readings on radials which need further investigation etc etc.
if time allows, might be a good idea to take a few Zs readings and end/end continuity of RFC/S.
Reply to multi consumer board changes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
What certification do I need when replacing a consumer unit ? Here are the details. I am semi retired (electrician) and work for a company as...
7K
This is getting embarrassing - I've been looking for a sub-main consumer unit in a church for an hour now. I've found the incomer. There's a nice...
6K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
  • Locked
5K