DNS1

-
Esteemed
Reaction score
771
Under what (if any!) circumstances is it permitted to run two separate cables to make up the conductor surface area of a larger cable (which, in this case is impossible to install...

Need to change 2 6mm radials for a single 10mm, but it's going to be near enough impossible to draw through a new cable due to lack of access to the route....

Are there any loop holes in the regs which will allow me to use the existing cables?

Excuse what's probably a really stupid question, I mainly do temp installations these days... Festival sites etc, so never have to overthink access and making do with what's already there!
 
what's the cable/s feeding? it's common to use 2 cables in parallel for distribution circuits. If they are final circuits, could yo make them into a 6mm rfc?
 
Hi - To make use of 2 conductors for 2x the current carrying capacity it’s important they both be the same length so the current is equally shared. In your case it may just be easier to run your new cable as 10mm and be done, just saying.
 
Cheers for the help everyone.

In this case, it's removing two 8.5kW electric showers (in adjacent bathrooms, being fed off the same unit, via the same route) and replacing with a single high powered unit in one of the bathrooms.

It's in T+E and both runs will be almost exactly the same length.

Considering the hassle of replacing the cables, if needs be, I'd be happy to put a small CU in the cupboard next door, use the existing cables as a distribution circuit and run a final in 10mm from that to the shower itself.

The whole RFC idea isn't something I'd considered earlier... I've never done one in anything other than 2.5mm!
 
If your calculations (accounting for installation method etc) showed that two identical cables of 5mm2 would be sufficient (for example), then if you had two cables of 6mm2 in parallel, they would be slightly overrated.

If the cables are not quite exactly the same length, the current would be shared inversely proportional to their resistances. It should be possible to work out what imbalance in lengths was permissible before one of the cables started to be overloaded due to taking too much of the current.

I'm not offering to do the calculations, but my guess is the odd few percent difference in lengths would be perfectly OK.
 
Cheers for the help everyone.

In this case, it's removing two 8.5kW electric showers (in adjacent bathrooms, being fed off the same unit, via the same route) and replacing with a single high powered unit in one of the bathrooms.

It's in T+E and both runs will be almost exactly the same length.

Considering the hassle of replacing the cables, if needs be, I'd be happy to put a small CU in the cupboard next door, use the existing cables as a distribution circuit and run a final in 10mm from that to the shower itself.

The whole RFC idea isn't something I'd considered earlier... I've never done one in anything other than 2.5mm!
what's the rating of the new shower? and the reference method that the 6mm cables are installed
 
I'd be happy to put a small CU in the cupboard next door, use the existing cables as a distribution circuit and run a final in 10mm from that to the shower itself

You don't need a CU, just a junction box. Preferably locate it so that the lengths of the 2x 6mm² runs are equal, but don't bust a gut over the last inch or two!
 
Look up parallel supplies in the regs. As far as I know the rules are same CSA cable, sample cable type, same length, same route.
 
Technically it can be done, but the question is should it be done?

With parallel conductors there is always a risk that a fault on one conductor will leave the other conductor(s) overloaded. With two T&E in a house which may, or may not follow the exact same route, there is a higher chance of damage occurring to one cable than there is with cables installed for the purpose of being parallel conductors.

I personally wouldn't be inclined to do it as it is unconventional, and unconventional in a domestic installation often leads to trouble down the line.
 
if it saves a ball-ache installing a 10.0mm cable, then, although unconventional, I can see no problems as long as installed and terminated correctly, esp. to avoid overload on 1 leg, I can't see why not. notmuch different than a RFC for sockets.
 
Technically a shower on a ring ,just feels wrong .
Frugal.
(long term reliance on it's perfection -makes it dangerous)
if it saves a ball-ache installing a 10.0mm cable, then, although unconventional, I can see no problems as long as installed and terminated correctly, esp. to avoid overload on 1 leg, I can't see why not. notmuch different than a RFC for sockets.

It wouldn't be a ring, it would be a radial circuit made up of two parallel cables.
 
It still needs testing like one ( with access to measure loop !)
(or current clamp individuals to check balance ?)

No it doesn't, you can't test it like a ring with only one point in it as far as I can see.
I've never tested parallel cables like I would a ring, and can't see how you could?
 
Just reread the initial post.
Other than checking the book, my worry would be the next person who makes it unsafe as they cant work out what's done.
 
Last edited:

Reply to Multiple cables in place of one in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
On this commercial building we are refurbishing it has the above fire alarm panel which I think is pretty much brand new, I'm not even sure it was...
Replies
6
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
806
I have had a kitchen extesion built on an old property (c.1810), which has an unusual consumer unit situation. Part of the property has only a...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock