I have a 2.5mm supply in a loft and from this i have it going to a FCU which I then have my lighting mains for a switch coming from the load side of FCU , I then go from the FCU to 4 different sockets and then last in line I have to connect to another FCU for the bathroom heater downstairs , is this acceptable? (This would be a radial circuit as only one leg up from board for supply )
 
So long as it’s CPD is 20A and you meet disconnection times that sounds fine.
 
Pg 188 of the OSG refers - max CPD on a 2.5mm radial is 20A due to the cable only being rated to 27A.
 
Pg 188 of the OSG refers - max CPD on a 2.5mm radial is 20A due to the cable only being rated to 27A.
NB - you said 'loft' in your OP which implies insulation, so check your derate factors as well!! It's 27A at method C, not buried throughout in itchy-scratchy stuff.
 
Yes there is plenty insulation up the loft as is with most lofts but my cables are clipped to the top of the joists as floor in new loft is being raised so think I should be okay as cable not directly buried in any insulation.
 

Reply to Multiple FCU on radial? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock