rabbroon

if anyone knows about immersion heaters ? got economy 7, but my bottom immersion nay heating the water during the night, its getting 240v when the off peak supply comes on but does not heat up! I took a resisitance reading getting 35 ohms off the live to neutral,! just to check I tested the top immersion where I got 17 ohms. Does this mean the bottom element has kicked the bucket?
 
if anyone knows about immersion heaters ? got economy 7, but my bottom immersion nay heating the water during the night, its getting 240v when the off peak supply comes on but does not heat up! I took a resisitance reading getting 35 ohms off the live to neutral,! just to check I tested the top immersion where I got 17 ohms. Does this mean the bottom element has kicked the bucket?


Measure the resistance across the element and via the stat
 
If the element measures 35 ohms it's going to consume roughly 1.5 kilowatts. This might be correct, I'm not sure to be honest.


Really you need to check the current flowing though the element and compare this to the kilowatt rating written on the element. I'd also run an IR test but you'd need a mega tester to do this. If you're unsure about safe isolation or if you don't have the test equipment then call an electrician rather.
 
Test across the element and you should get 18-19 ohms then measure across live and neutral as it comes into the element cover ie before the stat and you should get the same if not your stat may have a problem.

Well done for referencing the top unit as this is exactly the same as the bottom one so if that is working ok then thats a good reference point
 
Right both are 3kv immersions! the top one the Boost supply has 17ohms reading on the live and neutral coming in the immersion and also 17ohms across the element itself however the bottm immersion has 35 ohms in the incoming supply and 35 ohms between the live and neutral through the element! So do we agree that there is something up with the off peak immersion and needs replacing?
 
I'd remove the bottom element and visually check it, the 35 ohms reading isn't right for a 3 kW element. Also check for limescale build-up in the tank whilst the element is out.
 
Not the thermal cut out if its giving 35 ohms across the element. 17 ohms is about right for a 3KW element so I would suggest the one at 35 ohms is replaced.
 
I'd remove the bottom element and visually check it, the 35 ohms reading isn't right for a 3 kW element. Also check for limescale build-up in the tank whilst the element is out.

Marvo he is in Scotland we don't do limescale up here the same as we don't do Part P!sh
 
Right both are 3kv immersions! the top one the Boost supply has 17ohms reading on the live and neutral coming in the immersion and also 17ohms across the element itself however the bottm immersion has 35 ohms in the incoming supply and 35 ohms between the live and neutral through the element! So do we agree that there is something up with the off peak immersion and needs replacing?

Just do what I said in my post ie test on the element and then through the stat you will not have a high limit on the stat
 
Not much difference between 17-35 ohms....if the element had gone would suggest a full o/c or a least a higher reading than 35 ohms. if the element had burnt out would suggest a short circuit to earth
 
Lol, I'm in Cape Town so my knowledge of Scottish water is limited, I read somewhere it's the same colour as beer :)

Could never understand why we threw money to the electronic plants because they threatened to go to England only problem was the they used a lot of RO water I know because I worked in one because it was easy to filter our soft water. Mind I still chuckle when I see descaler kits in the local diy shed
 

Reply to my bottom immersion nay heating the water during the night in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi, My flat uses an Economy 7 tariff. When I use the boost heater, it works fine. But the off-peak water heater doesn't heat up the water...
Replies
11
Views
2K
I get the feeling asking this will produce head shaking, I'll ask anyway... I have a hot water tank with a single immersion heater. Currently...
Replies
7
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Yes a friend is trying to get as much low cost energy as possible, he has a water tank with top and bottom elements which runs of Economy7 through...
Replies
3
Views
1K
I am in a bit of a pinch at the moment and trying to argue a massive amount of used of electricity with my provider which I find it hard to...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock