short story, I've come across a 3 phase distribution circuit wired in 4mm singles on 63a hrc fuses. I found this because 1 of the phases was on a 20a and had blown. this seams wrong to me but as I said I don't have much ind experience. this is a new circuit from a tap off box. also I don't want to drop someone in the rubbish if it is wrong.
 
So one phase was 20A and the others 63A? If they are pvc singles contained in conduit they are only rated at 28A. If they are thermosetting (BS7211) they are rated at 44A.
 
Who would you be dropping in the crap that so concerns you and why do you priorities this against both public and property safety?

My next concern is you are getting involved with situations you have little to no experience in, it may be the fact that overload protection of the cables is not afforded due to an exemption found in the BS7671 regarding fixed load equipment, this could be what you have come across although it's also common to find bodged work and poor design so with knowing all the details of electrical install and the load itself it's hard to call on whether it complies or not and if it's a hazard.
 
the person I don't want to drop in it, is who ever connected the 4mm to the 63a fuse. the omission of overload protection was what I was thinking of but as a distribution circuit I can't see how that would apply (my lack of experience). the 3 lives have been clamped and read 17, 15 and 26a respectively. this is not my problem to fix but I feel I should raise my concerns if they are justified.
 
What is it supplying, it is not just overcurrent protection but the issue of the conductors withstanding fault current.
 
Those conductors are undersized, with a dist board there is no way of knowing any future loading, but if alterations/additions are carried out hopefully a competent person SHOULD see the situation. Theoretically there is a possibility that with any future loading those conductors could seriously be overloaded.
 

Reply to my industrial inexperience? in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello everyone, I’m based in the ROI and live in a rural location. Yesterday evening my electricity supply started to switch on and off randomly...
Replies
2
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
759
After my last post and having and having to re-learn some stuff can someone check and advise on a few things. Sorry if this is wrong don't hate...
Replies
7
Views
2K
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock