Hi all , after some opinions on N-E fault or ring main.
After chasing this fault and ruining my bank holiday weekend , ring main IR readings as follows
L-E >999
L-N>999
N-E>0.98Mohm
I have narrowed it down to a cable spurred from ring main , astonishingly the 3no. Cables in the twin switched socket all individually test out at >999 across all conductors. It’s only when connected together that it causes the low reading , like there is a low resistance between 2 different cables ,any ideas?
TNCS supply , split load consumer unit
After chasing this fault and ruining my bank holiday weekend , ring main IR readings as follows
L-E >999
L-N>999
N-E>0.98Mohm
I have narrowed it down to a cable spurred from ring main , astonishingly the 3no. Cables in the twin switched socket all individually test out at >999 across all conductors. It’s only when connected together that it causes the low reading , like there is a low resistance between 2 different cables ,any ideas?
TNCS supply , split load consumer unit