Typical classroom clown. Wouldn't last 5 minutes in the real world, and wouldn't make a brass farthing either. Midwest has got it right, any continuity is 90% of the way there.......
OSG does suggest a figure of 0.05 ohms, GN3 states 'the resistance values obtained should be of the same order......'. I can obtain a difference of more than 0.05, if I take a reading with the test leads attached, and then a different reading applying pressure to the clips.
In a new installation, I would expect identical results (r1+rn). In older installations, that tolerance maybe in a higher magnitude. And in older installations, there is more chance deteriorating terminals, inaccessible JB's or unseen diy work. Its what you chose or what the customer chooses to do about it, is the issue.
"Typical classroom clown" - this is exactly how it's taught these days and the 0.05 figure is quoted in GN3. Dismissing advances in technology and teachings, especially in an ever evolving business such as electrics, seems like a silly approach to me.
Edit: 0.05 is quoted in OSG not GN3
You wait until you are out in the real world and see how silly it is. I could take you to a dozen older properties round here and do an RFC test, and guarantee that the R1 and Rn readings would be further apart than 0.05 ohms. are you going to spend hours (days even) pulling up floors and god knows what else in each one? Or are you going to use a bit of common and move on. Its like Midwest says, you can get those sort of differences by jiggling the test leads around. If they are widely different, then yes there is a problem that needs investigation, but not 0.05 ohms. You have to remember that a lot of lecturers have never operated in a real environment. You have to balance what you are taught with actually making a living."Typical classroom clown" - this is exactly how it's taught these days and the 0.05 figure is quoted in GN3. Dismissing advances in technology and teachings, especially in an ever evolving business such as electrics, seems like a silly approach to me.
Edit: 0.05 is quoted in OSG not GN3
You wait until you are out in the real world and see how silly it is. I could take you to a dozen older properties round here and do an RFC test, and guarantee that the R1 and Rn readings would be further apart than 0.05 ohms. are you going to spend hours (days even) pulling up floors and god knows what else in each one? Or are you going to use a bit of common and move on. Its like Midwest says, you can get those sort of differences by jiggling the test leads around. If they are widely different, then yes there is a problem that needs investigation, but not 0.05 ohms. You have to remember that a lot of lecturers have never operated in a real environment. You have to balance what you are taught with actually making a living.
Your right, I shouldn't have used that term, and I have regretted it ever since actually. Unfortunately I couldn't edit it, the guy in question has written some excellent books a couple of which I own and often refer to. It is just the fact that there is a lot of difference between the classroom environment and the real world, as born out this afternoon! although not too great an example I measured 0.44 for R1 and 0.51 for Rn. Now, I believe that most people, me certainly, would think "1960's property, original wiring, iv'e got a difference here of 0.07, jackpot. As you say, a judgement call would be made depending on how far out it might be if it were higher, but I still think this 0.05 guideline is a bit unrealistic unless it is a fairly new installation. You have to weigh up the time it could take to find and remove all the accessory fronts, the damage you might do in so doing (grouting and so on), the difficulty (under kitchen units with 3 inch screws disappearing into a black hole), and then the likely-hood that it is probably going to be a junction box under an oak wardrobe stuffed to the gills. To say that such things are easily remedied in 15 minutes is utter nonsense, as has been muted.I fully understand and actually do agree with you. I'd expect older properties to be quite a way apart from a new installation in terms of readings, I just think the rebuttal of "classroom clown" is a bit harsh seeing as though that is the standard for newer installs.
Ultimately though, if you know it's an older installation and are receiving these sorts of readings then that's to be expected and noted. However, surely there's no harm in stating to the customer that while those sort of readings are expected for an installation of that age, if it were a new install then you'd expect a lot better?
That's where the discrepancy of being experienced comes in. The ability to differentiate between expected readings and new values being taught.
Your right, I shouldn't have used that term, and I have regretted it ever since actually. Unfortunately I couldn't edit it, the guy in question has written some excellent books a couple of which I own and often refer to. It is just the fact that there is a lot of difference between the classroom environment and the real world, as born out this afternoon! although not too great an example I measured 0.44 for R1 and 0.51 for Rn. Now, I believe that most people, me certainly, would think "1960's property, original wiring, iv'e got a difference here of 0.07, jackpot. As you say, a judgement call would be made depending on how far out it might be if it were higher, but I still think this 0.05 guideline is a bit unrealistic unless it is a fairly new installation. You have to weigh up the time it could take to find and remove all the accessory fronts, the damage you might do in so doing (grouting and so on), the difficulty (under kitchen units with 3 inch screws disappearing into a black hole), and then the likely-hood that it is probably going to be a junction box under an oak wardrobe stuffed to the gills. To say that such things are easily remedied in 15 minutes is utter nonsense, as has been muted.
The regulations have tolerances states designed to ensure safety. If readings are outside those tolerances then something isn't right.
Then i would put down on the report as a code 3 and moveAnd what about when it is in some long-forgotten accessory that even the home owner is unaware of, or a JB hidden under the floor, or god-knows where else? 10-15mins???