NAPIT Certification Scheme napit code 2/3
Discuss napit code 2/3 in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net
hi guys i spoke to nappit recently after reading their codebreakers book,it said code 2 for all cables which are buried in the wall less than 50mm deep not rcd protected.i then said when doing a eicr i have always coded lighting circuits not rcd protected as code 3, he then said you would have to around with a cable tracer to make sure all cables are within zones and unless you can prove that then it would be code 2,your thoughts guys
Bizzare. Cables buried in the fabric of the building is not part of the test?!
it's on the tick sheet under RCD additional protection. 5.12 - 3rd line.
wot he sed. ^^^^^. C3 all day (at worst). wood butchers and wet-pants will drill into them, presrcibed zones or not. the more we kill, the better.
I agree c3 all day for that!
This really annoys me about these technical help lines and codebreaker book, an inspection is to prove that it is safe for continued use and pick up any things that may not now comply due to regulation changes! It is an opinion based on experience expertise and knowledge with physical testing. The code given is down to the opinion of the inspector and situation surrounding it. These books are the opinions of others that cannot see the situation you are applying the code to. This is why we have indemnity insurance!
Does anybody go around with a cable tracer? Never heard of this before to prove cable within zones
Dean in the USA we have a company come out free of charge who has a wand that finds underground utilities plus where they are, talking foundations we have to secure our earth to the rebareb before they pour their concrete
Well the updated best practice guide 4 has it as a C3 still and considering Napit along with the Niceic and other bodies in the industry have banded together to write this thing, I find it bizarre that the Niceic give it a C3( this was a question asked on a Facebook live stream) and Napit a C2 ( from their code breaker book).
For my 2 pence worth I give this a C3 personally.
C3 for me, in general.
Maybe we're getting to the point, though, if the property was wired to later 17th, C2 could come into it.....but in such a case it should be RCD protected anyway...so there's already a C2 for that. If you think about it, you could save an awful lot of C2's with an RCBO. As regards zones, why would you want to check them for an EICR?...unless the plaster's falling off the wall and showing things up.
Maybe we're getting to the point, though, if the property was wired to later 17th, C2 could come into it.....but in such a case it should be RCD protected anyway...so there's already a C2 for that. If you think about it, you could save an awful lot of C2's with an RCBO. As regards zones, why would you want to check them for an EICR?...unless some of the plaster's falling off the wall.
That's why I put it on here as I couldn't understand
I don't believe that installation date should come into it. Assess the risk and code accordingly. And lack of RCD additional protection where now required cannot be given no recommendation code.
C2 in you’re opinion?
I certainly wasn't suggesting that! But was correcting someone who advised no code and someone else who suggested that a 17th Edition install should be C2 (implying that older installs shouldn't). It would be a C3 for me.
Reply to napit code 2/3 in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hi all, first post so go easy! This is for people who are looking for more info on the course and exams and is from my experience of doing the...
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Another what code! This is in conjunction with an EICR I have just carried out. 9.5kW shower on 6mm and 32A MCB. Been in place for a long time...