Discuss Need some help with ring final circuit please!!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

first. continuity of each of the 3 conductors end to end. if it's 2,5mm with 1.5mm cpc, then the resistance of the cpc will be approx 1.67 x that of each phase conductor. that is r1, rN, and r2.

then connect each L to the other leg's cpc at the CU. measure at each socket between L and E. the readings shoul all be the same, unless you have a spur. that is your R1+R2.

then IR at 500v

that's your dead tests. then you have the live tests, Zs, PFC.
 
first check end to end on all conductors
them take live from one leg and earth of other leg(if t+e a leg is each t+e)and connect together
then oppisite live eaths and connect together
take ohms reading from this two conections
each socket that is on the ring should have the same reading (not alway exactly)any that have wildly high readings are spurs (this is also your R1+R2 reading
do this again using live and neutral which will also prove polarity
hopr this helps
 
Last edited by a moderator:
first. Continuity of each of the 3 conductors end to end. If it's 2,5mm with 1.5mm cpc, then the resistance of the cpc will be approx 1.67 x that of each phase conductor. That is r1, rn, and r2.

Then connect each l to the other leg's cpc at the cu. Measure at each socket between l and e. The readings shoul all be the same, unless you have a spur. That is your r1+r2.

Then ir at 500v

that's your dead tests. Then you have the live tests, zs, pfc.


so in step 2, it say that (r1+r2)/4 ? Is the value from step 1, end to end should divided by 4?
 
yes, if you divide by 4 that will give you what to expect for R1+R2, but you still need to measure it.
 
so in step 2, it say that (r1+r2)/4 ? Is the value from step 1, end to end should divided by 4?

Yes.

The value's of r1 & r2, obtained in step 1 are added together. Then divide the result by 4.
The resultant value will be the expected figure obtained on all the socket outlets incorporated within the ring final, spurs will most likely be higher.

There are other variables to consider but this is the basic principle.
 
To do the Zs = Ze+(R1+R2),, to get the Zs is the value from step 1,end to end should be use? without dividing it by 4
 
no . the end/end is r1 and r2. to calculate Zs you use R1+R2. this is the reading you get when cross linking the legs.
 

Reply to Need some help with ring final circuit please!!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
471
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
795
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
788
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
820

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock