Was talking to someone today about a radial from the CU to a single garden IP rated socket. TN-S supply.
I was thinking that I would run 3-core SWA from the garden socket into an indoor adaptable box and from there in T+E back to the CU. The SWA runs underground across a lawn.
In the adaptable box I was just going to link the armour to the circuit CPC to provide a return earth path. However he reminded me that as the SWA is entering the building from outside, the armour, although insulated, is an extraneous conductive part, and therefore must be connected directly to the MET via 10mm bonding cable. To be honest I can't remember ever seeing main bonding attached to SWA armour before.
It does make sense to me, so is this correct?
I was thinking that I would run 3-core SWA from the garden socket into an indoor adaptable box and from there in T+E back to the CU. The SWA runs underground across a lawn.
In the adaptable box I was just going to link the armour to the circuit CPC to provide a return earth path. However he reminded me that as the SWA is entering the building from outside, the armour, although insulated, is an extraneous conductive part, and therefore must be connected directly to the MET via 10mm bonding cable. To be honest I can't remember ever seeing main bonding attached to SWA armour before.
It does make sense to me, so is this correct?