Discuss Neons on IR test ..... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

jules27

Maybe common sense ,but I'm still learning . Even if you switch the spur off will the neon still ruin your IR reading , they wont be illuminated and therefore not connected or only connected on load side.

thanks
 
think you are right. if you switch off the spur/isolator, your IR tester will not see the neon
 
the neon will we disconnected ont the live side of spur/isolator so will not be seen on the ir test but will be seen on the switched side!
 
As per regs in BRB you can use other methods if you can't disconnect equipment vulnerable to testing

Clamp Line/Neutral together and test to Earth

Under certain circumstances even a 250v test is acceptable
 
As per regs in BRB you can use other methods if you can't disconnect equipment vulnerable to testing

Clamp Line/Neutral together and test to Earth

Under certain circumstances even a 250v test is acceptable

I wouldn't class a neon as vulnerable equipment, they are on the load side so just turn off the switch and note on your cert NEON next to the circuit.
 
Are they wired between L/N or L/E ? Not all fused connection units have any double pole switch, and what if the FCU is protecting a radial or other down rated hard wired circuit ? like a small lighting circuit, you wouldn't be IR'n the whole circuit, although having re- read the OP I assume he is protecting fixed equipment so switching off would do the job
 
They are wired between line and neutral. You don't need a double pole switch to isolate them.
If they are protecting a radial then you should really bypass them and complete the tests, but common sense would prevail.
3 things I hate: 1 Neons, 2 Dimmer Switches and 3 down lighters :p
 
Your obviously a professional electrician so I can't tell you how to suck eggs, but do you not find method 2 of doing IR saves all that aggro of disconnecting Dimmers, trannys and socket based RCD's etc ?
 
Please explain, not looking for an argument, but to expand my knowledge of Inspection and testing.

612.3.1 BRB

Top of page 38 GN3 and page 39 GN3

Both appear to acceptable methods
 
There is no test between L1 and LN on method 2, and it is usually a soft test at 250V that is emloyed with this method..... I wouldn't call the removal of a neon for test purposes as unreasonable or impracticible. As has been stated switching off the switch is not necessarily going to test the full length of fixed wiring, but in the same vein testing L1 + LN to L2 is not a thorough test.

Just pull the neon, people. It's not difficult.
 
Test opinion 2 should only be used when there is vulnerable equipment that can not be removed or it is impractical to remove it. Basically test method 2 is a worst case scenario, you should always do a full IR test as described in GN3, OSG, and the BRB.
 
Thanks fellas I think I get the jist now

Where poss do test 1

Where not poss do test 2

However I would refer you to the NIC guidance learning course that states

" That normally IR is measured between Live conductors L/N and E, Exceptionally however for for a PIR IF it is impracticable to remove electronic devices from the circuit a measuring between to protective earth only should be made with Line and Neutral connected together.

Thanks for your input it has been really interesting, it seems on a PIR, it may be acceptable but not on a Initial or addition.

ATB Steve
 
I shouldn't pay too much attention to an NIC course book, look at GN 3 and the BRB, doing a PIR would also be different from an initial verification. You could get away with method 2 on a PIR as it will be impractical to remove vulnerable equipment etc and you are looking to get a general assessment of condition in relation to the installation.

As for Initial verification you should always use method 1.

Hope this has helped?
 
It has really helped fella's I plan to be top of my game so I try and sort wheat from the chaff, I ask questions not to be difficult but to challenge and get to the bottom line on the best advice, so I am very grateful of your answers and all taken on board.

Many Thanks S
 
Unlikely deterioration of insulation ( Pvc )
Extensive and expanding use of functional earths,electronic controls,neon lights,low voltage equipment
RCDs on most (domestic) installations
Material properties that are far in advance of what was available in the past

A sample list of why the insulation resistance test is fast becoming an un necessary or at the least, a less important test than we would be ready to accept

It is also becoming a possible "danger to equipment" test
In the near future, possibly the rule makers may have much less emphasis on this hyped up test than there is at at present

It doesn't have the importance it once did,especially initial verification
The cable insulation will either be sound or a connection or damaged cable will not be sound
Things like damp ingress into equipment, is more often than not picked up by Rcds
Low readings of insulation values are mostly confined to the likes of older installation materials


Insulation resistance ?
"remember when we used to do those tests" :)
 
I'm glad you described my post as an observation,because that is all it was meant to be :)
I will be clear and say that whilst the rule makers say it is important, then I will follow sheepishly

I made the post because the arguments for and against the method of doing this test,didnt mention the reasons for the test at any time

I do believe that the test is of much less importance than earth continuity or Ze or Pfc
The extreems that are suggested to carry out this test goes well beyhong what I personally would carry out for an initial verification

I believe changing a consumer unit is a different kettle of fish
By the very nature of the job,it is for older or outdated installations where the insulation resistance test becomes more important because of older materials deterioration and unknown damp and earth fault possible problems

After all its just an opinion,but also a chance to broaden the subject of the thread :)
 
I think you should look upon an insulation resistance test on initial verification as a quality check, whilst it is unlikely a brand new length of PVC cable will have a problem, it is not beyond the realms of possibility.

Then on older installations it is a useful tool in determining the condition of the installation.
 

Reply to Neons on IR test ..... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
545
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
605
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
710
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
773

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock