the above formula would be correct for a live to earth fault.

N to E fault depends on the loads that are being drawn at the time (creating an imbalance in the voltage between N and E and therefore a current flow between them)
 
the above formula would be correct for a live to earth fault.

N to E fault depends on the loads that are being drawn at the time (creating an imbalance in the voltage between N and E and therefore a current flow between them)

the above formula would be correct for a live to earth fault.

N to E fault depends on the loads that are being drawn at the time (creating an imbalance in the voltage between N and E and therefore a current flow between them)
A dead short of lets say 0.2 ohms N-E without current will not open RCBO, with a load it will open.

Now if the fault was >7666 ohms, with current will the RCBO open.
 
Think about how an rcd operates.

It is a simple comparison between live current and neutral current.

An imbalance between those measurements of >30mA will cause it to trip.

It is not possible to give a resistance between N and E that will cause it to trip or not trip.

A fairly low resistance fault could be tolerated if there is zero load on the entire installation
As loads increase, not only on the circuit protected by rcd but also others, a combination of parallel paths and differing volt drops in parts of the installation can cause it to trip.
 
Think about how an rcd operates.

It is a simple comparison between live current and neutral current.

An imbalance between those measurements of >30mA will cause it to trip.

It is not possible to give a resistance between N and E that will cause it to trip or not trip.

A fairly low resistance fault could be tolerated if there is zero load on the entire installation
As loads increase, not only on the circuit protected by rcd but also others, a combination of parallel paths and differing volt drops in parts of the installation can cause it to trip.
I'm not talking about imbalance, which we know is how an RCD operates. So forget that for now.

I'm talking about a Neutral to Earth resistance that is greater than 7666 ohms. On load will it open the RCD ?
[automerge]1594834846[/automerge]
Anything less than 7666 ohms on load will open the RCD.
 
I'm not talking about imbalance, which we know is how an RCD operates. So forget that for now.

I'm talking about a Neutral to Earth resistance that is greater than 7666 ohms. On load will it open the RCD ?
depends on the load, that is what creates the imbalance
 
Like I said in my first post, 7.6k is the maximum live to earth fault value that can be tolerated
 
an impedance of 7666 Ohms would be the absolute maximum impedance like equivalent max Zs for a RCD if you ever had an impedance of 7.6 kiloOhms there is a serious problem.
Indeed sir, it shows degradation of the insulation.
Max Zs is 1667 ohms on a 30mA which is touch voltage of 50V.

In doing EICRs its impossible to disconnect everything, especially with lighting loads.
[automerge]1594835934[/automerge]
Like I said in my first post, 7.6k is the maximum live to earth fault value that can be tolerated
James the OP states N-E
 
C4F60519-4BEC-4B59-9369-3CBD51E8940E.jpeg
so to trip the rcd Il needs to be different from Ina by greater than 30ma
Ina= In-If
If is dependant on both the load Rn, and the parralel resistors Rfault and Rn (nutrual conductor resistance.)
the 7.6k value you are mentioning would cope with a load of zero ohms or a dead short.
 
any impedance under 7.6k will allow 0.03Amps you would need a maximum insanely high impedance of above 7.6k for there to be a problem so 7.6k is the maximum impedance that can be allowed etc.
 
B9D3481E-5A88-4144-8294-127B990D0CAB.jpeg
now here is where it gets a little complicated.

depending on the other loads Rext and the resistance of the bond between E and N, the voltage of the N line can vary.
if it goes up, some of the current from Rext will pass back through the rcd and down the parallel path through Rn and Rfault SUBTRACTING from the current passing through the neutral line on the rcd.
this will INCREASE difference between Il and Ina and help the rcd to trip.
 
Last edited:

Reply to Neutral to Earth in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
639
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
581
So I’m an apprentice and I’m just trying to get a better understanding of the science behind this because the electricians who have said it have...
Replies
12
Views
1K
So, I was messing around yesterday with some old testers I have laying around to see if they still work I found my dads old Robin MFT and noticed...
Replies
8
Views
510
Hi, I carry out PAT testing on landlord appliances for letting agents in rented accommodation. Occasionally some of the items I cannot access...
Replies
5
Views
694

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock