Hi all, ive been asked to add 2 extra socket to the ringmain in an office, the office is on a 32a mcb.

all cabling is surface so will i need an rcd/rcbo

if it was a new circuit i agree i would then need one, but do i need one for just adding sockets of existing circuit??

if yes this is going to push the cost up sky high and i will proberly then loose the job :(
 
not sure on the UK rules -it's 30MA here automatically


but you need to be careful in an office environment of introducing nuisance with a single rcd/rcbo
 
Well that depends on what the sockets are going to be used for and who has access to them. If you look in the regs book and find that they do need to be rcd protected then you may be able to use RCD sockets.
 
411.3.3 RCD required unless the socket outlets are for use under the supervision of a skilled or instructed person or are labelled for a specific item of equipment. ;)
 
Last edited by a moderator:
Your Additions still have to comply to bs7671 2008.
 
Hi all, ive been asked to add 2 extra socket to the ringmain in an office, the office is on a 32a mcb.

all cabling is surface so will i need an rcd/rcbo

if it was a new circuit i agree i would then need one, but do i need one for just adding sockets of existing circuit??

if yes this is going to push the cost up sky high and i will proberly then loose the job :(

I am inclined to agree with Jud on this one to some extent. I aint going to go and get the book out but if my memory serves me correctly the cables dont need RCD protection as they are in trunking, surface mounted etc, but you would need to provide RCD socket outlets.

You say it will push the cost sky high......RCD's and RCBO's are coming down in price. Stick an RCBO in for the ring it will only push the cost up by about £30, cheaper than a handful of RCD outlets.

Cheers........Howard
 
Last edited by a moderator:
Hi jud

just been on the link makes very interesting reading ( additions /alterations on a 3036 fuse wire ) at the discretion of the electrician if rcd needed ( new socket near back door ) or socket in front room just need to fit rcd socket and not rcd whole circuit makes fitting a extra socket backt to £ 100.00 and not new board ect £ 350-500 roll on july 2011 and the big green book

Rich
 
Although 7671 requires that all sockets rated at 32a or less must be RCD protected the get out clause is the line 'unless for use of skilled persons or persons under supervision.
If the sockets are to be used for specific equipment rather than general use and that equipment is supervised by say the IT manager.....in my opinion there is no need to RCD them. I also consider that in an office environment it is undesirable to RCD them as nuisance tripping can cause significant problems and disruption.
The sockets you install should be labelled as not RCD protected and not for general use

If the installation method that YOU use is surface trunking (regardless of the rest of the circuit)then RCD protection for the wiring will not be required,if you conceal cables at a depth of less than 50mm and not enclosed in earth metallic conduit etc then RCD protection will be required and this would probably mean in practice RCD-ing the whole circuit..
 
Last edited by a moderator:

Reply to New sockets existing ring in the Australia area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
971
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
657
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
278
Hi, I would like to add a new socket in the bedroom. Current room configuration: 3 existing sockets - wiring coming from the bottom (under the...
Replies
1
Views
681

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock