Discuss New to testing... Ze, PSCC & PEFC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Good Good!
So on EIC..
I put in the "External Earth Fault Loop Impedance Ze" = 0.20
& For my "Prospective Fault Current" from my readings what would you put in the "kA" Box ???
Good Good!
So on EIC..
Yep and the PFC box you put your highest value of PEFC or PSCC which is 1.01.
Odd though as normally on a TNCS they are near enough the same, but dont worry about that for now!
So from my readings you'd put in "1 kA"
and the maximum this can be is 16.5kA, Is this correct?... and this will be written in the "Short Circuit Capacity" Box on the EIC?
Ok Nature of Supply etc.
External EFLI Ze is the max so for TNCS its .35 There is then a box underneath for Measured Ze
PFC Single phase is what you measure so 1.01kA
Short Circuit Capacity is normaly 33kA for BS 1361 Type II 100A fuse.
Ok thanks J.. I dont know where ive got 16.5 from, ive seen it the max for something.
Where in the red book would i find these figures?
Hi Magic-sid
Do you have a lock off kit ? Remember switch off & lock off ! you will fail your assessment if you dont.
Regards
Kung.
Thought you were locking off with gorilla glue or no more nails lol
See not that hard onece you know mate ! best of luck with assessment !
Regards
Kung
Yer me neither when i get in the kids and mrs are like that thing off dr who the Obsorbatoff or summit they drain all the sence out of me !
Reply to New to testing... Ze, PSCC & PEFC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hi guys and gals, I have a question about the leads to computers (commonly known as kettle leads). I am new to PAT testing so please bear with...
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...