• IMPORTANT: Please note that nobody on this forum should be seeking from or providing advice to those who are not competent and / or trained and qualified in their field (local laws permitting). There is a discussion thread on this global industry-wide matter HERE. This also has more information about the warning with regards to sharing electrical advice in some countries. By using this forum you do so in agreement to this.

Discuss NMD 90 in aboveground Conduit in the Canadian Electricians Only area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:  American Electrical Advice Forum

Can you put NMD 90 in conduit aboveground? Looking to run 6/3 NMD 90 to spa pack from garage. Garage is completely finished, this is the easiest way and I also have a piece of 6/3 leftover from a renovation.

Thanks in advance
 

Megawatt

-
Arms
Can you put NMD 90 in conduit aboveground? Looking to run 6/3 NMD 90 to spa pack from garage. Garage is completely finished, this is the easiest way and I also have a piece of 6/3 leftover from a renovation.

Thanks in advance
Hahner just because it’s # 6 it doesn’t mean it’s good for 65 amps it depends on the insulation and if you pull cable in a conduit it still has to be approved for wet locations
 