Tested a kitchen ring today and got continuity on Line, Earth but not neutrals. Tester wouldn't give reading on R1 + R2 but everything else (Ins res, Zs, RCD trip time etc) was in order. Got 230v at each socket outlet and think I know where the problem lies (buried in wall with a brand new kitchen and tiling covering it:eek:). Being newish to testing, what aret he issues with having no continuity on the neutrals and is it safe to leave this till later next week as unable to attend before then.
 
S

sparkyork

you could always temporarly split the ring somewhere bout halfway, and put the ring on 2 16a radials till you get chance to sort it?
 
C

Cirrus

  • Thread Starter Thread Starter
  • #3
Trouble is the site manager can't get me back there until Wed at the earliest and I have to remove tiles, kitchen units (high level) base units, work top, just to get to the plaster.
 
S

sparkyork

ahh i c, is it an empty new build? or if not then you might just have to keep your fingers crossed! lol saying that tho ive seen countless radials backed up by a 32a mcb so im sure it be ok till you get there on wednesday, i could be wrong but i think if you cant get a ring on the neutrals then think you'll have to split it to radials?
 
C

Cirrus

  • Thread Starter Thread Starter
  • #5
It's a council refurb. Major works to sort the problem. Looks like a Thorsman crimp has failed!! Absolute crap!
 
S

sparkyork

oh dear! i got some crimps the other day and as soon as you put one end in it pushes the inner bit out the other end! really frustrating!
 
C

Cirrus

  • Thread Starter Thread Starter
  • #7
I have used crimps successfully for years but these Thorsman crimps are poop.
 
P

pope

  • Thread Starter Thread Starter
  • #8
SPlitting the ring sounds slike the best option, i ahve done it befor where it would cause alot more disruption ripping off tiles and hacking at plaster. Then having to have plasterer back and tiler back.
 
S

Shakey

  • Thread Starter Thread Starter
  • #9
you could always temporarly split the ring somewhere bout halfway, and put the ring on 2 16a radials till you get chance to sort it?
i would do the same, but use 20A MCb's - Table 8A (16th OSG), or appendix 15 17th ed springs to mind:rolleyes:
 
G

Grae79

  • Thread Starter Thread Starter
  • #10
had same prob myself not too long back but was on the live/phase/line...relatively easy fault find.....turned out to be bad connection in back of socket, thankfully.
 
J

jimes

  • Thread Starter Thread Starter
  • #11
would splitting the ring at any point other than the failing crimp not give a bad neutral connection on the "new" radial?
 
C

Cirrus

  • Thread Starter Thread Starter
  • #12
Yeah that is exactly what I was thinking. Only way to rectify is to remove units, tiles and plaster and try and locate failed crimp.
 