I went and did a visual inspection on a flat. No Rcd protection present.

10 mm earth to water and gas was connected.

No sign of supplementary bonding. So i did a long lead test and found that all pipe work in kitchen and bathroom was below 0.05 Ω.

Does this mean no supplementary bonding is required?

Ive advised the board be upgraded but dont think they can afford it
 
R

RISElectrical

Cant afford a board change but can throw money away with a visual inspection? unless you did it for free
 

tony mc

Electrician's Arms
Messages
1,426
Location
North of London South of Edinburgh
I would not worry about the kitchen as its not required under BS7671.

In addition to reg 701 and doubt exits re the effectiveness have a look at reg 415.2.2 but you will need to do some testing to establish if it is connected in the bathroom!

Hope this helps!
 

tony mc

Electrician's Arms
Messages
1,426
Location
North of London South of Edinburgh
Yes then supplementary bonding may be omitted as long as the 3 conditions are met as per 701.414.2.

This is where the Visual Inspections are worth nothing IMO as the only way you can establish the above is by getting you test equipment out!
 