I went and did a visual inspection on a flat. No Rcd protection present.
10 mm earth to water and gas was connected.
No sign of supplementary bonding. So i did a long lead test and found that all pipe work in kitchen and bathroom was below 0.05 Ω.
Does this mean no supplementary bonding is required?
Ive advised the board be upgraded but dont think they can afford it