Discuss No isolation of Neutral in Single phase boards in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
13
As title.

Doing an EICR, have come across a couple of DBs, where the neutral goes straight onto the bar on Single phase boards.
Whats your views on this guys?
Should it have a requirement to be isolated? Is there a reg for? If so then it can be coded.
My boss thinks its dangerous. I don't, but I'm happy to have a school day.
The boards have stickers on them, stating supply must be isolated elsewhere before taking cover off as well.
Thanks
 
Only required on TT earthing arrangements.
 
If ordinary persons are using the equipment which equates to households then the main switch must isolate all poles.
The job is a commercial one.
[automerge]1599567757[/automerge]
There is also an argument that the DB should be isolated elsewhere before removing cover. As we know its illegal to work on live equipment.
Also there are a lot of OPDs that are single pole.
 
Last edited:
If ordinary persons are using the equipment which equates to households then the main switch must isolate all poles.
Just thinking...what about domestic 3 phase boards? 4 pole isolators?
I suppose it depends on the situation.

Just as an aside....I wonder if Part Peees have been issued for work on some of them big houses (Buckingham and Windsor, for instance).
I'll bet the NIC say they should.

Or Houses of Parliament......plenty sleep in there and call it 'home'.
 
I have a Hager 3-phase Invicta in my house with only a 3-P isolator switch - ie the neutral is not switched on the board. I was told that the 4-pole disconnector next to and between this dis-board and the meter is sufficient. Would you agree?
 
I have a Hager 3-phase Invicta in my house with only a 3-P isolator switch - ie the neutral is not switched on the board. I was told that the 4-pole disconnector next to and between this dis-board and the meter is sufficient. Would you agree?
As long as the 4 pole switches the 3 phases AND the neutral, then, yes, it’s sufficient. That is the main isolation, not the 3p on the board.
 
I have a Hager 3-phase Invicta in my house with only a 3-P isolator switch - ie the neutral is not switched on the board. I was told that the 4-pole disconnector next to and between this dis-board and the meter is sufficient. Would you agree?
It's generally not desirable to interrupt the neutral on a three-phase system, unless it's a TT system.
 

Reply to No isolation of Neutral in Single phase boards in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
914
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hi everyone, I want to repurpose an old cable that was previously used to power a 3-phase machine. The cable is 4L1.5 micc, and I don't want to...
Replies
7
Views
1K
Hi all, new to this thread and just looking for some views. I have today attended a industrial unit which is being converted into small...
Replies
8
Views
2K
Guys in a solar PV plant room I have a single phase LV board for power and lighting. This is fed via 2 phases off a solar inverter through a 415 >...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock