Hi, as I've said I'm not an electrician but studying C&G in my own time and have worked as a mate.
I've just had a qualified sparky upgrade my CU to a split board 10 way dual RCD. He has run a 4mm2 cable (from a 40A MCB protected by one of the RCDs) to my hut and will be coming back to wire up a sub main for a radial with a couple of double sockets and a light circuit. He says he is fitting a sub board whose main switch will have no RCD (since the circuit is already protected by the RCD form the main board?) I don't understand that. Can someone help? BTW, I couldn't find the DIY section to post this.
 
TL;DR
rcd sub main
Test Meter - Forum Sponsors since 2007!
This official sponsor may provide discounts for members

littlespark

-
Arms
Esteemed
If any circuit has an rcd at its origin, it doesn’t need another one.
2 rcd’s in-line like that can cause a lot of head scratching if there’s a fault....

4mm to a hut? What’s in there? Sounds like a lot of power for a potting shed
 

Andy78

-
Mentor
Arms
Esteemed
If you're studying then performing a cable calculation for the hut feed could be a useful and enlightening experience.
A said, the RCD affords it's protection for all circuits downstream of it, it will detect imbalances in the hut distribution circuit and all the associated final circuits so another RCD in the hut is not necessary.
 

buzzlightyear

-
Arms
Esteemed
yes you are correct ANDY,but if a fault in the shed or their abouts the RCD will fail and what ever that is on that rcd in house will go off has well.but i did not design it .
 
  • Thread Starter Thread Starter
  • #10
If any circuit has an rcd at its origin, it doesn’t need another one.
2 rcd’s in-line like that can cause a lot of head scratching if there’s a fault....

4mm to a hut? What’s in there? Sounds like a lot of power for a potting shed
Thanks for the prompt reply. Potting shed......I have great plans :)
Post automatically merged:

Wow, that was quick and thanks for the prompt responses. I agree that the 4mm cable (rated at 37A) is overkill. By my calculations on a load of say 4KW gives approx 18A and since there is little need to allow for derating factors (wooden framed man cave) then 2.5 mm (rated at 27A) would be enough, but if this is wrong please let me know.
 
Last edited:

davesparks

-
Mentor
Arms
Esteemed
Thanks for the prompt reply. Potting shed......I have great plans :)
Post automatically merged:

Wow, that was quick and thanks for the prompt responses. I agree that the 4mm cable (rated at 37A) is overkill. By my calculations on a load of say 4KW gives approx 18A and since there is little need to allow for derating factors (wooden framed man cave) then 2.5 mm (rated at 27A) would be enough, but if this is wrong please let me know.
The problem is that if the cables maximum rating is 37A then the largest standard size ocpd it could be connected to is 32A, it is not suitable for a 40A ocpd unless overload protection can be omitted, which it can't for a submain.

I think you have some terminology confused in your OP, 'submain' is the common term for a distribution circuit. So a submain generally refers to the cable and associated ocpd which forms the circuit feeding a distribution board.
 
  • Thread Starter Thread Starter
  • #13
The problem is that if the cables maximum rating is 37A then the largest standard size ocpd it could be connected to is 32A, it is not suitable for a 40A ocpd unless overload protection can be omitted, which it can't for a submain.

I think you have some terminology confused in your OP, 'submain' is the common term for a distribution circuit. So a submain generally refers to the cable and associated ocpd which forms the circuit feeding a distribution board.
Thanks for taking the time to reply. After studying a bit more I can see what you mean. We have Ib = 18A, In = 40A and Iz = 37A. We need to have Ib<=In<=Iz so these numbers fail. Should have used 32A MCB - am I correct?
 
  • Thread Starter Thread Starter
  • #15
I dont have cable calc charts but I would have thought only 4 mm cable that might take 40 amp might be MICC
Thanks for taking the time to reply. I didn't mention that in my OP. It is 4mm MICC. I found this bit of the chart online..........4mm - 40amps method 1, 42amps method 11
 

davesparks

-
Mentor
Arms
Esteemed
Thanks for taking the time to reply. After studying a bit more I can see what you mean. We have Ib = 18A, In = 40A and Iz = 37A. We need to have Ib<=In<=Iz so these numbers fail. Should have used 32A MCB - am I correct?
The cable should have been sized correctly for the selected OCPD.
A soloution now could be to use a 32A OCPD, but I wouldn't use an MCB if it can be helped.
 

davesparks

-
Mentor
Arms
Esteemed
Thanks for taking the time to reply. I didn't mention that in my OP. It is 4mm MICC. I found this bit of the chart online..........4mm - 40amps method 1, 42amps method 11
Are you sure? That is a very odd cable to use for a domestic installation these days considering it costs around £10/m
 

James

-
Mentor
Arms
Supporter
Esteemed
Wow, I am surprised, not many of us out there that know how to gland off micc cable now days. Seems a surprising choice of cable for a domestic setting.
 
  • Thread Starter Thread Starter
  • #19
The cable should have been sized correctly for the selected OCPD.
A soloution now could be to use a 32A OCPD, but I wouldn't use an MCB if it can be helped.
Thanks again. As I've said, I'm not qualified so what alternative to an MCB would there be bearing in mind a 10 way dual RCD Hager board has just been fitted by my electrician
 

davesparks

-
Mentor
Arms
Esteemed
Thanks again. As I've said, I'm not qualified so what alternative to an MCB would there be bearing in mind a 10 way dual RCD Hager board has just been fitted by my electrician
A switchfuse seperate from the main CU then an RCD CU in the outbuilding would be a better choice from the point of view of selectivity and minimising disruption in the event of a fault.
 
  • Thread Starter Thread Starter
  • #21
Are you sure? That is a very odd cable to use for a domestic installation these days considering it costs around £10/m
I'm not sure whether its MICC but I attach an image of what they've run to my hut. None of the cable is exposed to the elements.
micc.jpg
 
  • Thread Starter Thread Starter
  • #32
Just a big thank you to you all. I know "a little knowledge is a dangerous thing" and having a little knowledge would certainly apply to me, but I'm still learning and you guys help greatly.
 

AJshep

-
Arms
Esteemed
Either way Hi-tuff has not got an earthed metallic covering (like SWA) so it will need to be protected at source by an RCD like he has. Just not ideal its attached to the same RCD thats covering some of your house circuit's
 

ipf

-
Mentor
Arms
Esteemed
Hi-Tuff is a good alternative to swa in some circumstances.
Question is, is the cable being run underground to the shed? If so, it's not an option, due to insufficient protection.
How old is the consumer unit? Is it possible to alter and feed via RCBO?
 
  • Thread Starter Thread Starter
  • #35
Hi-Tuff is a good alternative to swa in some circumstances.
Question is, is the cable being run underground to the shed? If so, it's not an option, due to insufficient protection.
How old is the consumer unit? Is it possible to alter and feed via RCBO?
Thanks for replying. The cable is cleated to joists through my shop store to the shed attached to the shop store. At no point is it underground. As in the OP, the consumer unit fitted by my sparky is a brand new Hager 10 way dual RCD
 

ipf

-
Mentor
Arms
Esteemed
Thanks for replying. The cable is cleated to joists through my shop store to the shed attached to the shop store. At no point is it underground. As in the OP, the consumer unit fitted by my sparky is a brand new Hager 10 way dual RCD
OK, then.
As regards the Hager, I'm not positive, but would think it's possible to create a non RCD protected section. 20/32 amp RCBO should be fine.
 

davesparks

-
Mentor
Arms
Esteemed
Either way Hi-tuff has not got an earthed metallic covering (like SWA) so it will need to be protected at source by an RCD like he has. Just not ideal its attached to the same RCD thats covering some of your house circuit's
That doesn't necessarily mean it needs to be protected by RCD.
This would only be required for the cable if it was chased in to a wall at less than 50mm deep, so if it is clipped direct as it appears then its not needed.
 

AJshep

-
Arms
Esteemed
That doesn't necessarily mean it needs to be protected by RCD.
This would only be required for the cable if it was chased in to a wall at less than 50mm deep, so if it is clipped direct as it appears then its not needed.
Agreed. For some reason I was under the impression it was buried.
 

Reply to No RCD in sub main in the Electrical Forum area at ElectriciansForums.net

Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Aico 3000 Range
This official sponsor may provide discounts for members
Top Bottom