Changing contactor,this one clatters & buzzing.
Will put a report in,can you see the red 2.5m single cable,this comes off the LIVE side of the contactor,control for this circuit.
The Mccb protection for this circuit,which supplies a TPN DB rated @ 200 amps.
Any ideas how to protect this control circuit.
 

Attachments

  • FCD42D9E-30D8-4918-8147-3D9170A9CADD.png
    3 MB · Views: 46
Changing contactor,this one clatters & buzzing.
Will put a report in,can you see the red 2.5m single cable,this comes off the LIVE side of the contactor,control for this circuit.
The Mccb protection for this circuit,which supplies a TPN DB rated @ 200 amps.
Any ideas how to protect this control circuit.
Slide lock fuse and carrier, fitted in the contactor control circuit.
 
You will need to find out what the control circuit is supplying to figure out the size of fuse/circuit breaker to fit, a double pole one will be needed to switch both live and neutral
 
You will need to find out what the control circuit is supplying to figure out the size of fuse/circuit breaker to fit, a double pole one will be needed to switch both live and neutral
Why DP? May be a 400v control circuit no N, unlikely but has been known
 
Last edited:
Looking at the picture, there are 2 wires from L1 and N.
Not sure what the control circuit is feeding. I presume that at it is 3 phase it will be industrial.
In my opinion breaking live and neutral together is safer.
 
Looking at the picture, there are 2 wires from L1 and N.
Not sure what the control circuit is feeding. I presume that at it is 3 phase it will be industrial.
In my opinion breaking live and neutral together is safer.
It’s 230v ctrl not sure yet what it’s doing.
Still abit naughty coming off LIVE like that.
 
i once had excessive chattering bashing my lugholes. i divorced her.
 
I think the control cables should be closer to the size of the main cables feeding in.
That would be a better practice
The control circuit has lower consumption therefor a smaller cable suitably fused down should be employed, sorry for the red cross by the way, if it's a large load say for example fed by 10mm cable are you suggesting using 10mm cable for the control circuit as well?
 
I think the control cables should be closer to the size of the main cables feeding in.
That would be a better practice
Sorry for the disagree red cross Mate, but a main circuit sized conductor for the control circuitry, apart from be unnecessary is impracticable, have you ever tried getting main circuit sized conductors, say above 2.5mm2 cable into the coil/pushbuttons etc terminals?
 
The control circuit has lower consumption therefor a smaller cable suitably fused down should be employed, sorry for the red cross by the way, if it's a large load say for example fed by 10mm cable are you suggesting using 10mm cable for the control circuit as well
A silly practice I think Steviec 1:
The control circuit has lower consumption therefor a smaller cable suitably fused down should be employed, sorry for the red cross by the way, if it's a large load say for example fed by 10mm cable are you suggesting using 10mm cable for the control circuit as well?
Not at all,imagine f a fault developed at the point where the main cable enters the isolator/contactor. If the main cable is 25mm and the control cable is 2.5mm, there is a danger that the smaller cable could suffer "burn out". This could result in a fire!!
The control feed at this point should ideally be the same or at least 50% of the size of the main cable until it reaches the circuit breaker or fuse for the control circuit.
Of course ideally the cables of dissimilar size could be fed from a busbar system and bolted seperately, this would negate the problem.
 
Not at all,imagine f a fault developed at the point where the main cable enters the isolator/contactor. If the main cable is 25mm and the control cable is 2.5mm, there is a danger that the smaller cable could suffer "burn out". This could result in a fire!!
The control feed at this point should ideally be the same or at least 50% of the size of the main cable until it reaches the circuit breaker or fuse for the control circuit.
Of course ideally the cables of dissimilar size could be fed from a busbar system and bolted seperately, this would negate the problem.
Only if the fuse /mcb didn't operate
 

Reply to Noisy,buzzing contractor in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
579
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
514
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Hi guys, A car showroom / workshop brand we do work for has asked us to modify a few things in the workshop. One of them being to implement...
Replies
7
Views
907
Hello everyone i recently got a job on replacing a BMS panel in a plant room. the NEW panel i installed except the control side of the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock