Discuss nuisance tripping of 100 NSX Schneider MCCB in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Evening Gents

i have a 4 pole schneider mcb which keeps tripping intermittently the overload is set at 80A and runs in delta at around 40 A.The mcb supplies a 3 phase pump rated at approx 50kw-any one got any ideas what the problem could be .
cheers.
 
Re: nuisance tripping of 100 NSX Schneider MCB

what type is the MCB?
 
Re: nuisance tripping of 100 NSX Schneider MCB

What are you pumping?

What type of pump are you using?

Is is there anything common between it tripping?
 
Re: nuisance tripping of 100 NSX Schneider MCB

The circuit been designed by someone who is clueless about motor circuits... it will continue to nuisance trip because the mcb is not a good choice to cover a 50Kw motor regardless of mcb type or starting methods, you will be better using HRC fuses and its not a matter of matching the fuse to the loading of the motor, it doesn't work like that, you will need to have experience and knowledge in circuit design and the characteristics of the motor.


Anything exceeding 22Kw should not really be on an mcb and even a 22Kw would need a 63(d) mcb for a standard motor and starting duty... this brings big problems complying to Zs unless you oversize the cables.
 
Re: Schneider MCB tripping cont

Hi gents same question would you protect a 50kwpump motor with mcbs or hrc fuses
dripping


I'd protect it with a cover or build a pumphouse. Just joking, complete lack of info.

Softstart?
VFD?
Application?
Type of pump?
New install or existing?
Test results?
 
Re: nuisance tripping of 100 NSX Schneider MCB

There is
A problem with both mccbs I was wondering could there Bea problem with a cable from the common feed being loose and while the circuit is cold there is no problem but when cables heat up the resistance will go up and possibly cause overheating overloading across 2phases and tripping the install action
 
Re: nuisance tripping of 100 NSX Schneider MCB

There is
A problem with both mccbs
What do you mean by both mccb's? Why are there two of them?

I was wondering could there Bea problem with a cable from the common feed being loose and while the circuit is cold there is no problem but when cables heat up the resistance will go up and possibly cause overheating overloading across 2phases and tripping the install action
That's quite a wild theory. If there's a problem with a cable then you'd see evidence in the test results or during a visual inspection. If the cable is the correct CSA for the load then it won't heat up to a point where it's resistance changes significantly enough to affect the characteristics of the circuit.
 
Re: nuisance tripping of 100 NSX Schneider MCB

Your posts so far are extremely confusing. Maybe rewind back to the beginning and tell us what there was before you arrived, what was the reported fault, what tests you did and why the cable has been replaced.
 
Evening Gents

i have a 4 pole schneider mcb which keeps tripping intermittently the overload is set at 80A and runs in delta at around 40 A.The mcb supplies a 3 phase pump rated at approx 50kw-any one got any ideas what the problem could be .
cheers.
Approx 50kW?
The nearest standard motor would be 55kW and have a FLC of about 105A at 400V.
It us usual on pump sets for the motor to be rated at close to the pump requirements.

Typical no-load current for a three phase cage motor is about a third of FLC. If the motor is running at 40A, that suggests that it is almost off load entirely.

Unless I'm missing something, your information doesn't add up.
 
The code didnt register the op gave but yes its an mccb ... OP used the term mcb ...totally different tripping curve ...I would consult tech of mccb and ask what recommended rating for motor is... also check if it has adjustable settings other than Amps ,they may be set up incorrectly...

This thread is lacking so much info it cannot really progress without the OP giving a detailed breakdown of all the points raised.
 
Am I correct saying not ALL of the compact NSX range has thermal protection? I thought some of them only have magnetic which isn't suitable anyhow.
 
Last edited:

Reply to nuisance tripping of 100 NSX Schneider MCCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
I'm in France and this is my first post, so apologies if this is in the wrong section. Here is the problem. I have a client, with a swimming pool...
Replies
14
Views
3K
How do you size the MCB, wire and protection for a motor in the UK/Europe? How is it typically done...
Replies
22
Views
7K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock