Looking for a little advice.
I was speaking with a colleague who was confused about a circuit design that doesn't offer much selectivity.
A sub main is being fed via a SWA to a 63A commando style outlet which is to be used for temporary set ups (shows, Marquess etc).
The circuit is protected at circuit origin via a 30ma RCBO. All events that are plugged in use our little temporary boards which are movable. These temp boards have a little C/U with 4 circuits each. All circuits are again 30ma RCBO's.
My colleague was concerned that in the event of a earth fault on a circuit, there is no selectivity on which RCBO would trip. It would be a nuisance if the RCBO supplying the 63A outlet was to trip. I suggested possibly a time delayed RCBO at the circuit origin, however under the 18th all outlets up to 63A require 30ma rcd protection and I'm pretty sure you can't get a time delayed 30ma RCBO.
Any advice?
True. And in all fairness, there is nothing to say an SWA needs Rcd protection.
As Strima says document a RA. Insisting all circuits plugged into the commando socket must be RCD protected and possible having it labelled as such would be sensible mitigating examples.
Reply to Numerous RCD's, selectivity in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...