Discuss Nurse Call System in the Industrial Electricians' Talk area at ElectriciansForums.net

S

surreysparks

Hi All

I have a random problem with a C-TEC 800 nurse call system.

The sounders are not working, even though when the alarm is raised they receive 14VDC.

When I attach the pair from the sounders that is in the panel and connected to the sdr outlet to a toner you can hear both the sounders so I know they work.

Confused.....
 
Carnt say I have any experience of the c tec system but I know that some of the older fire alarm systems use to flip the polarity of the sounders to switch them on or off

That's just a total shot in the dark I have no experience of the c tec nurse call system
 
There is a common Neg and positive from the control panel to all sounders, plus a signal cable which is the zones trigger, you are allowed upto 3 sounders per zone. allcall points are just neg and trig

That sounds about right to me, though i've never even heard of the C-Tech nurse call system, let alone have any experience of them...
 
We deal with alot of nursing homes for fire and nurse call although the c-tec 800 is not widly used. most of them Eng54 are just and adressable system like the fire alarms
 
The sounders they have are 1 pair, no trigger etc....


As tazz has uploaded the wiring instructions for the C-Tech 800 system in his post #4, look at the wiring connection requirements for the different sounder options. They can't be much clearer, for you to be able to sort it out from there!!!
 
Remote I beleive just a - and a +.

They get 14v, no noise.

Connect the paid from my toner to the + and - at the panel and they make noise....

So the sounders work.

They get voltage when a call is raised, but don't sound...
 
No idea about the system itself, but have you measured the voltage when in alarm, whilst it is connected to the sounders? IT may drop off significantly when under load.
It is possible that the supply is not man enough to provide enough current to operate the sounders, either from the panel design or the length of run
 
Ok there is your problem, you can only switch remote sounders from a sounder switch unit, they cannot be connected on the zone. But you can connect direct to the panel SND + and com - All calls will activate the sounders.
 
C-tec produce a variety of 800 compatible nurse call systems, which model are you actually using here?

They have different connections for different models.
You do have the sounders connected in parallel not series don't you?
 
I have posted the instructions for you, and explained the switched and line driven sounds......So what do you want this system to do which has not been explained
 
I changed the wiring from sdr - and + to using one of the com.

Sounder(s) get 14v but there is the slightest noise from them.

Sounders have an in and an out.
 
Are the sounders C-tec 800 series.....C-tec have two on the market....800 series standard zone and Quantec addressable 2 wire. can you give me the part number for the ssounders you have
 
Are the sounders C-tec 800 series.....C-tec have two on the market....800 series standard zone and Quantec addressable 2 wire. can you give me the part number for the ssounders you have

The sounders do not appear to have a part number, they merely have sounder or something written on the front and a 2 pole in and out on the rear.

They have an adjustable volume.

The terminals have seen better days, so im hoping to rewire from the first to the second sounder and replace them, and hope that this would sort it out?
 

Reply to Nurse Call System in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
Replies
38
Views
4K
Hi, My alarm system is a Texecom control unit (Premier 64-w) + Keypad + Sounder, and is using the wired zones 1-4 only, with no additional...
Replies
2
Views
2K
Hi I’ve recently installed a texecom veritus excel alarm system but having an issue with the sounder not going off when triggered by the pir I’ve...
Replies
16
Views
2K
Daughter has bought a house and it has a home security system, G-Tag setup. Issue is the alarm panel displays are pixelated and you cant see...
Replies
0
Views
633
I am doing renovation to a cafe in Scotland at the moment and after speaking to the local council the building requires the minimum standard for a...
Replies
5
Views
993

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock