Called out to repair some cabling today. Cable Tv guy has drilled through the ring main cables, completely severed one and nicked the insulation on the other. Old metal clad CU with 4 rewirable fuses, all found intact but the 60A main fuse had blown. Hacked out the scene of crime and decided to do temp repair, checked the ring continuity and ok on L & N but no continuity on earth. Reconnected the three and retested and found that I had 8 ohms live to earth and same on neutral. Continuity still ok on L/N but none on earth. Disconnected and left a section that tested ok
It was nearly seven pm so we have left as a radial on 15a, can't quite get my head round it at the mo, any thoughts? Is it possible that the cable has been damaged elsewhere?
 
Very likely yes. The PFC has let through and taken out the mainfuse PFC on a dead short woild mean the whole ring has taken a hammering, and with the csa of the cpc being smaller that will suffer, and show up any weakness at terminations throughout the install. Your going to need to investigate further to find your gremlin.
 
Called out to repair some cabling today. Cable Tv guy has drilled through the ring main cables, completely severed one and nicked the insulation on the other. Old metal clad CU with 4 rewirable fuses, all found intact but the 60A main fuse had blown. Hacked out the scene of crime and decided to do temp repair, checked the ring continuity and ok on L & N but no continuity on earth. Reconnected the three and retested and found that I had 8 ohms live to earth and same on neutral. Continuity still ok on L/N but none on earth. Disconnected and left a section that tested ok
It was nearly seven pm so we have left as a radial on 15a, can't quite get my head round it at the mo, any thoughts? Is it possible that the cable has been damaged elsewhere?

If a 60A fuse was blown, it's quite possible that the cpc has blown apart somewhere along the circuit, possibly damaging the insulation on L+N at the same time!

Did you do any IR testing?
 
Yep I am back am and will split and test.... No point in doing IR when its 8ohms to earth! Agree absolttely re RCD's! Apparently the cable guy was an electrician....and he walked!
 

Reply to Odd fault on ring main....your thoughts please! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
575
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock