Hi All,

Was testing a domestic installation prior to fitting a new cu:

1, No continuity on what appeared to be the a ring (was wired as a ring at cu), when i removed one of the legs (leg 1) I had L N reverse polarity at a spur (wired correctly), when I replaced the second leg (leg 2) at the cu the polarity was back to normal? Why would this be?

2. As mentioned there was no continuity between line conductors. But I had a reading of 20 Ohms between leg 1 and neutral at the neutral bar.

The house is a huge old place and has redundant circuits all over the place, bit of a nightmare to be honest rammed full of junk etc and difficult to get access.

Any ideas on the polarity issue,

Regards.

Simon
 
That continuity treading of 20ohms between L & N could indicate this is an Immersion heater feed and has been incorrectly wired up with one leg of the ring ...the other leg could be wired into a seperate fuseway. Try continuity test between leg 2 and any other 2.5mm2 cables at the board.


spark1
 
Thanks for he reply,

"Try continuity test between leg 2 and any other 2.5mm2 cables at the board."

I did that and got nothing, though Im off back on Thursday to take the place apart! I may be some time.

Regards
 

Reply to Odd Polariy Problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Legends, need some advice. I am a 12v automotive electrician, but have had a side project building a concession trailer for my dad. We have an...
Replies
6
Views
704
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
746
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
814
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock