hi all, just after a bit of advice have had a oil boiler fitted in a outhouse the company also wired it up. They took a 3amp fused spur off the the immersion spur ran 1.5mm 4 core 14 meters to outside junction box 3 meters of armored cable to another junction box then 5 meters in the out house to the boiler. Does this seem ok or do I need to get a electrician in. Thanks
 
Did you get any paper work from the company what showed they have tested the circuit, like a Minor Electrical Installation Works Certificate?
Have you paid up fully for the boiler?
Did they say why 4 core?
 
Waiting on the paperwork, the 4 core was because it needed a permanent live for a frost stat I think he mentioned it when quoting.
The other 2 companies that quoted advised the same junction box armored cable junction box but different cable sizes because the gap between the house and outhouse is about 3 meters had to go under the path.
 
My only concern is cable size and route, we had next door done 2 years ago which has identical boiler position but they run the cable in one complete length with no junction boxes armored cable I’m now wondering if that one is wrong and the new one is ok.
 
This is where pics can help folks to comment. Having said that, if it was able to be done in one run of cable there's less to go wrong over time.
 
I'm not sure why 4 core though.
It looks like the boiler needed a 3A supply which they took from the 3A spur. A 'permanent live for a frost stat' could be taken from the 3A spur that they have wired from, only needing 3 core.
If anyone is familiar with these boilers then maybe someone could correct me.

OP:
Are you using the switched fuse spur to switch on the boiler?
As above, a single cable would be better, but from what you describe, using junction boxes is not against regs... As long as it's been done correctly.
 
Would 1.5mm have been correct size?
I think the armored is because it runs under the flower boiler where the other house is all concrete.
Hi - let's say the load was 3A then voltage drop is
0.029 x 3 = 0.087V per metre (figures from Table 4D4A) . If I understand correctly you've about 20m run, so less than 2V drop in that length or less than 1% which is Ok.
 
Hi - let's say the load was 3A then voltage drop is
0.029 x 3 = 0.087V per metre (figures from Table 4D4A) . If I understand correctly you've about 20m run, so less than 2V drop in that length or less than 1% which is Ok.
too much information before beer o'clock. :D:D:D.
 
I'm not sure why 4 core though.
It looks like the boiler needed a 3A supply which they took from the 3A spur. A 'permanent live for a frost stat' could be taken from the 3A spur that they have wired from, only needing 3 core.
If anyone is familiar with these boilers then maybe someone could correct me.
.

A basic oil boiler normally requires a switched live, neutral and earth, the frost stat requires a permanent live. Therefore four conductors are normally required to a boiler in an outbuilding.
From the OP's description the fused spur is located in the house rather than the outbuilding so it's not possible to connect the frost stat directly to it.
 
This isn't a power circuit, it is part of the heating controls so is a control circuit.

Oh, ok. Must be the way the OP has described it in his post...
So where is the boiler getting it's power from... All confusing..
 
Oh, ok. Must be the way the OP has described it in his post...
So where is the boiler getting it's power from... All confusing..

I may have misunderstood the OP but I think the SFCU is in the airing cupboard with the rest of the boiler controls and wiring Centre and the cable in question is just the cable going to the boiler in the outbuilding
 

Reply to Oil Boiler cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all Mate of mine is getting a new utility room fitted, the kitchen fitting company have brought in their electricians for first fix and to be...
Replies
5
Views
2K
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...
Replies
1
Views
2K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
L
So my old man is planning on setting up a fish shed which will hold 2-3 fish tanks. The power drawn from the equipment which will be running in...
Replies
15
Views
2K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
540

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock