I am currently running around the country completing remedial work on the back of EICR's and have came up with a confusing pair of C2 faults as listed below:
My thoughts are to place an RCD at the source of the circuit + the switch needs replaced anyway so put a RCD-fused spur on.
Or would the RCD at the source be enough?
Or would the RCD-fused spur be enough?
The circuit in question feeds a small over-sink water heater in a unisex toilet. It would have very little use, the main building itself would only be accessed maybe once a month.
The earthing to the the accessories througout the building is all fed from steel conduit/trunking, overcurrent protection is from BS88-2 fuses.
Any thoughts?
Observation: Incorrect IP protection for accessories located in close proximity to a sink - WH Switch Needs Replaced - Corrision and Badly Rusted
Location: DB AS Circuit 3L2
Regulation: 512.2.1
Now? How would I go about this to tick off both C2's.Observation: Absence of RCD/RCBO protection for accessories located in close proximity to a sink
Location: DB AS Circuit 3L2
Regulation: 415.1.1
My thoughts are to place an RCD at the source of the circuit + the switch needs replaced anyway so put a RCD-fused spur on.
Or would the RCD at the source be enough?
Or would the RCD-fused spur be enough?
The circuit in question feeds a small over-sink water heater in a unisex toilet. It would have very little use, the main building itself would only be accessed maybe once a month.
The earthing to the the accessories througout the building is all fed from steel conduit/trunking, overcurrent protection is from BS88-2 fuses.
Any thoughts?