So abit of a random one. But yesterday my Neighbor asked me if I'd be able to take a quick look at their shower as it had stopped working. I said I'd go round an take a look and see if it was something simple enough to fix and get it going again.

Checked the usual things. The solenoid was fine, microswitch was working fine, no loose connections in the shower itself.

He said that it would work occasionally then would stop and that he has had to replace the pullcord 3 times in the past year

Took a look at the pull cord and noticed that the cables were mixed up. The supply was in the load and vice versa. I didn't see any burning, again no loose connections (this was a 45amp isolator.) And that one of the earth's were disconnected and wrapped in tape. Apparently it was like that the first time he replaced it.

I turned the power back on and got a reading of 170volts between line and neutral at the shower and 230 at the pullcord itself. The shower is fed by a 10mm cable covered by a 40amp MCB with RCD protection.

I just left it at that and told him to ring an electrician I know who can come out and test it to make sure that the RCD and all that will be working fine In case it's not working.Especially with only one earth connected.

But I'm confused. How can the shower only be getting 170volts at the shower when it's getting 230 at the pullcord? Unless it's broken?

Any ideas?
 
he has had to replace the pullcord 3 times in the past year
Red flag number one. This suggests more current is being drawn than the isolator is rated for, probably because of fault conditions.
And that one of the earth's were disconnected and wrapped in tape.
Red flag number 2
Someone might have found that connecting it trips the RCD.
I turned the power back on and got a reading of 170volts between line and neutral at the shower
Red flag number 3. This suggests a low resistance fault.

Someone needs to get busy IR testing this entire circuit. My long range prediction is a damaged cable between the isolator and the shower.
 
Just a suggestion-
If you were measuring 170V at the shower terminals, with a multimeter, but the shower was OFF, a high resistance fault (Megohms) in the circuit, say a carbonised/burnt terminal, could account for it. Turning the shower on would reduce the voltage to zero.
If you were measuring 170V with the shower running, that would indicate a low resistance fault, but with a couple of kW being dissipated somewhere, you would soon see where the fault was from the heat/smoke/flames!
 
Red flag number one. This suggests more current is being drawn than the isolator is rated for, probably because of fault conditions.

Red flag number 2
Someone might have found that connecting it trips the RCD.

Red flag number 3. This suggests a low resistance fault.

Someone needs to get busy IR testing this entire circuit. My long range prediction is a damaged cable between the isolator and the shower.
See, that's what I was thinking myself. Possibly a damaged cable or broken isolator again. As soon as I saw that wrapped up earth and the cable connected the wrong way around I knew something bad was up.

Glad I messaged my spark he's going round tomorrow to test it. He's local so he doesn't mind👍
 
Just a suggestion-
If you were measuring 170V at the shower terminals, with a multimeter, but the shower was OFF, a high resistance fault (Megohms) in the circuit, say a carbonised/burnt terminal, could account for it. Turning the shower on would reduce the voltage to zero.
If you were measuring 170V with the shower running, that would indicate a low resistance fault, but with a couple of kW being dissipated somewhere, you would soon see where the fault was from the heat/smoke/flames!
No if I switched on isolator and the shower I got 170. If it turned off either I got 0. If that makes sense. That's why I was confused.

I saw no burnt terminals.

Unless it's a junction box in the wall or attic or something?
 
Spark I work with is going round tomorrow to take a look. I'll report back what he finds. I might even tag along and annoy him for a bit. 🤣👍
This doesn't make sense to me either. What was the shower doing when you were measuring 170V across it? You said it was ON, but was water flowing, and if so what temperature was it?
i.e was it on as an 8kW+ load with water flowing, or was it just 'on' (but no water flowing, so not a load), in other words 'off'! 🤔
 
Last edited:
This doesn't make sense to me either. What was the shower doing when you were measuring 170V across it? You said it was ON, but was water flowing, and if so what temperature was it?
No, that's why I was confused. No water flowing at all no matter what setting I put it on. But the indicator light was on however it was very dim.

I even shut off the mains water and checked the filter and it wasn't blocked or anything. Again like I said solenoid was reading 3.5k ohms and the microswitch was working when I checked continuity across it.

It's a Triton shower if that makes any difference. Only reason I know to check the solenoid is the solenoid broke in my own Mira shower and I was able to fix that. Apart from checking those things I know very little about showers. 🤣
 
No, that's why I was confused. No water flowing at all no matter what setting I put it on. But the indicator light was on however it was very dim.

I even shut off the mains water and checked the filter and it wasn't blocked or anything. Again like I said solenoid was reading 3.5k ohms and the microswitch was working when I checked continuity across it.

It's a Triton shower if that makes any difference. Only reason I know to check the solenoid is the solenoid broke in my own Mira shower and I was able to fix that. Apart from checking those things I know very little about showers. 🤣
So I'm guessing no 8kW load from the elements is activated, because they haven't been turned on, because the solenoid isn't letting the water through because there's something like a 2.5 kohm fault somewhere in the supply acting as a potential divider with the 3.5k solenoid 🤔
So if I'm right (good chance I'm not!) there's about 40mA flowing in the faulty circuit with the shower "on". About 3 watts being dissipated somewhere!
 
Last edited:
So I'm guessing no 8kW load from the elements is activated, because they haven't been turned on, because the solenoid isn't letting the water through because there's something like a 2.5 kohm fault somewhere in the supply acting as a potential divider with the 3.5k solenoid 🤔
Only a minute current flowing. A much more likely scenario.
 

Reply to Only getting 170volts between line and neutral on shower? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K
Bit of a strange one ive been told by everyone ive called had a triton t70xr 8.5kw The water started running cold like the tco kicked in after a...
Replies
3
Views
1K
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
547

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock