B

beresford

Hi,
I have an open neutral problem within CU from the main-power supply to FCU (3A) to boiler. The voltgages of L(brown) and N(blue) on my boiler both appears as 238 v against earth. I tried to find where the neutral is open. I disconnected the three main-power lines (one red supposed to be live, one black supposed to be neutral and the yellow/green supposed to be earth) on the FCU (the other three lines to boiler also disconnected from FCU). I checked the voltage of these three lines from main power against the other earth which is grounded by connection to the metal panel of the boiler in the end.

Red the live against earth on boiler: 238
Black the neutral against earth on boiler: 147
yellow/green the earth from main-supply against earth on boiler: 178

Black against yellow/green the earth from main-power: 18
Black against red: 51
Red against yellow/green the earth from main-power: 36


I did some more tests. I connected both earths in FCU together and grounded it by connection to the metal panel of boiler.

Red against earth: 238
Red against black: 174
Black against earth: 37

I get confused now. Is the lines from main-power to FCU ok? Does the test suggest a short cut between the live and neutral somewhere from the air-switch box? why the voltage between the two earths isn't 0? Does it mean the earth from main-power isn't grounded?

Please help me. Thank you so much
 
Last edited by a moderator:
Turn the power off to this circuit and fault find by using dead tests.
You cannot identify a short by measuring voltages on an energized circuit, and lack of continuity is much easier to test using dead tester.
 
Last edited by a moderator:
Just a thought

Is your switch for your boiler on or off?
If its off then its switching N, turn the switch on and test again!

Otherwise turn all power off and do a continuity check between boiler and CU.


That will tell you what the situation is with the cables.

If the cable is broken you need a spark in to replace the cable between your boiler and CU.

If your Boiler has a 13A Plug and plugged into a Socket then check the plug, incase the wire has come off - same as the switch if its hard wired into a switch.



Looking at earth and earth
TURN IT OFF AND UNPLUG IT!

Get a spark out NOW and dont mess with it!

It will kill you if you come into contact with the earth!


So we know are you a sparky?

Also post your location on here so one of us in your area might be able to help!
 
isolate from supply. disconnect both ends, all 3 conductors. if you haven't got a wander lead, short all 3 at 1 end, then meter for continuity across the 3 at other end. all should read as short. then part the shorted ends and IR test.
 
Thanks for all. I did a bit more tests and edited my poster on top.
My boiler is off. I already took the pcb out after someone told me i have an open neutral problem. I am triing to find whether the broken happended between main-suppler-air-switch to FCU or between FCU to Boiler. I only connected the earth to the metal panel on boiler now.
I am so confused why the voltage of red against black isn't '0' if the neutral is broken happened between main-supply-air-switch and FCU or '238' if the CU between main-supply-air-swict and FCU is ok (174 and 51 dependant on the two earths connected or not).
I am aslo confused why the voltage between two earths is '178'. I am sure one earth is grounded.
I have not checked thecables on the main-power-supply-air-swich end.
 
You seem to have a urge to use a voltmeter to verify continuity
As said a continuity test should be a straightforward simple task to find this open neutral suggestion

Given you are sticking with this voltage detection,disconnect the neutral from the load on the fused spur,switch on or short out any switching in the circuit and test to earth,you should read mains voltage between the live and any reference earth and check for 230-e at the disconnected neutral
 
Thanks for Spartykus and everyone. sorry for reply so late. a very busy day.
I actually live in Cardiff.
I did the continuity for the cables between the boiler and FCU using a multimeter. The cables are fine. I connected the boiler to alternative power from a wall socket (I changed the 13 A fuse to 3A) and am very happy to find that the boiler still work although I already paid £100 for the parts that I won't use any more.

I have not done the continuity test for the cables between FCU and main-power-supply. I opened the air-switch box in the main-power-junction-box and have no idea why the colour of cables is different (red, black green, don't spot any loose coonection) from the colour in FCU-switch-on/off (red, black, yellow&green). I guess there is another juntion hidding somewhere for the cables between the FCU and main-power-supply. The neutral cable may be loose there.
I do have to find a professional to solvent the problem now.

Are you near Shropshire. I 'd love to find the fault for you
 
Last edited by a moderator:
Thanks. Could you please tell me what is spark? Is it used to conntect two wires? I tried to google information but no success.

Just a thought

Is your switch for your boiler on or off?
If its off then its switching N, turn the switch on and test again!

Otherwise turn all power off and do a continuity check between boiler and CU.


That will tell you what the situation is with the cables.

If the cable is broken you need a spark in to replace the cable between your boiler and CU.

If your Boiler has a 13A Plug and plugged into a Socket then check the plug, incase the wire has come off - same as the switch if its hard wired into a switch.



Looking at earth and earth
TURN IT OFF AND UNPLUG IT!

Get a spark out NOW and dont mess with it!

It will kill you if you come into contact with the earth!


So we know are you a sparky?

Also post your location on here so one of us in your area might be able to help!
 

Reply to open neutral problem please hlep in the Australia area at ElectriciansForums.net

Similar Threads

Hi, i’ve been trying to buy a smart switch 1 gang 1 way but i opened my conventional wall switch and i only have 1 red wire(Live Old UK) 1 black...
Replies
3
Views
513
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
648
Hello everyone, hope all are well. I'm changing a ceiling rose and have lost the diagram showing where everything was connected (to the old light)...
Replies
8
Views
905
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
608
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock