Discuss options for workshop supply in the UK Electrical Forum area at ElectriciansForums.net
just wondering what people would think would be the best way of doing this.
i have got to provide a supply up to a workshop in a garden (about 80 mtrs from the house). it will run underground all the way and then in the subfloor of the house that is currently being worked on all the way to the db.
What will the cable be supplying in the workshop, a single light and a double socket or a lathe and other heavy duty equipment?
The consumer is a fan of landrovers and that will be his garage for it. so there will be possibility of welders, grinders, lathes etc
i was thinking of putting the supply on 40amp mcb
80 metres is a substantial distance , will require a proper calculation imo
You could be looking at a 40a c curve mcb to prevent tripping
Due to the location heating may be a fair consideration of the loading , but I can just see a nice pot bellied stove. :)
It seems like he is going to be using this garage on a semi-professional bases/serious hobby/past time. Full due consideration needed especially if he has other enthusiast mates helping also using equipment plus the possibility of some heating/water heater. How big is this workshop?
I'd also be leaning to a fuse at the supply end. Any other services in this workshop such as water, gas etc?
It may be worth the customer enquiring of the DNO the cost of providing a separate supply to the garage. Depending on routing on their side, this may be relatively inexpensive and would give greater scope.
thanks everyone.
the garage/shed will be around 9mtrs x 10 mtrs.
their will most likely be water but no gas.
i will look into the possibility of getting a separate supply in
As you haven't provided a design current it is easier to use In. This also means you are covered for volt drop right up to the point of overload of the distribution circuit. 32A you could go 10mm, if you go 16mm, you can do 50A. Using In instead of Ib and youve got a VD just under 5% for both.
Check Ze. You have TNS so could be up to 0.8 ohms already....
C40 60890 max Zs is 0.54
R1+R2 for the 10mm is 0.35
R1+R2 for the 16mm is 0.23
Reply to options for workshop supply in the UK Electrical Forum area at ElectriciansForums.net
Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
190m run SWA underground, supplied from 3p+N 240mm sub main, each cabin total demand is 80A, worked out 35mm but volt drop is about 8%, would this...
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...