This has been rattling around in my head for some time, I have read the guide in the sticky section about exporting etc,so a building outside the equipotential zone should not have the earth exported, right ?, and a spike (s) should be used, but, what about the armour this should be terminated as norm but not connected to the parent earth ? but should it be connected at the slave end to the spike, Now I have seen in the past a spike at both ends the SWA armour terminated and spiked before entry to the parent building and the L & N brought in to the parent CU and thought mmm novel but does it comply? any thoughts anyone!
Pict
 
This has been rattling around in my head for some time, I have read the guide in the sticky section about exporting etc,so a building outside the equipotential zone should not have the earth exported, right ?, and a spike (s) should be used, but, what about the armour this should be terminated as norm but not connected to the parent earth ? but should it be connected at the slave end to the spike, Now I have seen in the past a spike at both ends the SWA armour terminated and spiked before entry to the parent building and the L & N brought in to the parent CU and thought mmm novel but does it comply? any thoughts anyone!
Pict

Where was that in the guide?

The building would need to be brought within the equipotential zone or provided with an earth electrode, the suppliers earth being isolated at the load end of the distribution circuit.
 
This has been rattling around in my head for some time, I have read the guide in the sticky section about exporting etc,so a building outside the equipotential zone should not have the earth exported, right ?, and a spike (s) should be used, but, what about the armour this should be terminated as norm but not connected to the parent earth ? but should it be connected at the slave end to the spike, Now I have seen in the past a spike at both ends the SWA armour terminated and spiked before entry to the parent building and the L & N brought in to the parent CU and thought mmm novel but does it comply? any thoughts anyone!
Pict

A TT with 2 spikes, that is not exporting and earth but perhaps tieing down to rods.
 
IQ You know I have I think mentall blocked the exporting thing as I have just re-read the guide and despite reading it over and over again I completley blanked the bonding conductor informatation, word blind or what !so in effect the armour will suffice as long as it complies with table 54H, sometimes the answer is right in front of you, despite having used this pratice in the past I have no idea why I was second guessing myself,
Pict
 
IQ You know I have I think mentall blocked the exporting thing as I have just re-read the guide and despite reading it over and over again I completley blanked the bonding conductor informatation, word blind or what !so in effect the armour will suffice as long as it complies with table 54H, sometimes the answer is right in front of you, despite having used this pratice in the past I have no idea why I was second guessing myself,
Pict

It's a topic that generates more questions and rumours than anything I've ever come across but if you just look at the basic component parts and the applicable regulations on earthing & bonding then all becomes clear.

In the vast majority of cases, using the suppliers earth is perfectly compliant but it can get expensive to meet the combined cpc/main protective bonding criteria so each case needs to be evaluated.
 

Reply to out buildings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
735
I’ve had a shipping container delivered to my building site for use as storage/utility room/worker toilet. One side is insulated as it was...
Replies
9
Views
8K
So I've just been reading through the electricians guide to the building regulations for my own knowledge and have come across 2 regulations which...
Replies
20
Views
3K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock