Just changed an outside light and was just questioning the max Zs allowed. It has been spurred off the ring main, switched fused spur with a 5A fuse in (existing). Final ring circuit is protected by a 32A MCB and RCD protection.
When carrying out Zs at the light fitting (cable runs under patio and up wall in conduit) I had a high Zs at 18 ohms. Tested using 'loop' on tester. When I checked using 'line' the reading was fine, so I presume it is a poor connection on the earth somewhere unless I am missing something?
I am going back tomorrow as I ran out of time today to check out why the reading was so high, as it is RCD protected theoretically it is acceptable, right? (1667) but I would rather find out the issue rather than relying on the RCD.
So when it comes to max Zs, do I go by a 6A MCB, or a 5A BS1361?
Appreciate any advice
Thanks in advance