Hi guys, bit of a strange one (long story). But do you know of any exceptions or any loopholes where you don't have to provide an outside socket with 30m/A RCD protection. (these sockets im talking about already have 100m/A protection anyway)
All general purpose socket outlets require 30mA RCD protection, and it does not matter whether they are inside our out. There are other considerations which will decide if you RCD the cables, or just fit RCD outlets.
Cheers..........Howard