Hi there,

This is my first post hope you can help. I have been asked to fit an outside socket so was going to split the kitchen ring main and loop to the outside socket then back to the kitchen ring. The CU is single RCD portected for all circuits and the outside socket is IP56 with RCD protection. Is this ok or will it have to be off a new circuit.

Thanks

rtonne10
 
Hi,

1st point : a spur from the Kitchen ring would suffice -no ring to extend the ring.

2nd point ; If you fit an RCD protected socket ,then you will have no discrimination in the event of an Earth fault on anything plugged into that socket , and the Main RCD in the C.U will almost certainly trip off also. :eek:

Just fit a Non-RCD protected socket and check the operation of the one in the fuse box for its rating [30ma] and for its effectiveness [ x1 & x5 tests]
You will have to make comment on the Cert as to the lack of discrimination---to fully comply you really ought to run a new circuit from Splitter block & 1-way RCD unit at the Consumer unit position.
 
run it as a spur from kitchen ring, as long as the cct is rcd protected then it will comply. Just ensure that the socket is the correct ip rating too.
as already suggested, dont fit an rcd socket due to discrimination.

:D
 

Reply to Outside Socket in the Australia area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
632
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
460
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
951
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock