could run them both off 6mm but want to have them on separate circuits and isolate them individually from the grid switch/CU. And nothing as its my own house.
It does not matter if its a Wendy house this part p melarky has been in since 2005 so
All new circuits need reg to the local building control.
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members
Aico 3000
telectrix

telectrix

-
Mentor
Esteemed
Arms
use the existing 6.0mm to a 45A cooker switch, then split off with 2 x 2.5mm radials, each on a 20A D/P switch.
 