- Reaction score
- 5,578
I've just spent an hour getting bogged down with the maths trying to work out diversity for 2 cooking appliances on the same circuit (32A MCB) and same isolation switch,
I thought I would give my workings so others can use it as I wonder if some just assume you can still use the 15kW maximum, which you can't.
In fact the the maximum for 1 cooking appliance seems to be 19.3kW (as long as the switch doesn't incorporate a socket), however, on with 2 appliances....
Diversity is 10A plus 30% of the remaining amps (plus 5A if a socket) but this is for each appliance even if on the same circuit.
Therefore for an oven and electric hob the maximum current we have is:
[10A + ( 0.3 x Q) ] + [10A + (0.3 x Q) ] = 32A
we don't know the maximum size of the cooker and hob (that's what we're trying to find out), so I have just used the letter Q (Q is the current of either the hob or cooker minus the 10A)
Therefore
The above equation is the same as
2 x (10A + 0.3Q) = 32A
20A + 0.6Q = 32A
0.6Q = 12A
Q = 20A
We know that each appliance is allowed to draw a max current of Q +10A, which is 30A. There are 2 of them so 60A.
60A x 230w = 13.8kW (approx)
Therefore maximum combined power for 2 appliances on same circuit with same switch (without a single socket) is 13.8kW.
I think you'll all have had enough now, but the maths works out as a maximum combined power of 10.4kW allowed if the cooker switch incorporates a single socket. (Equation is 25A + 0.6Q = 32A)
If you haven't guessed. I have the day off work! ?
ps.. would you check the maths please @happysteve
Therefore
20A + 0.6Q = 32A
0.6Q = 12A
Q = 20A