I am often installing two 3.5kw ovens in one kitchen which amounts to 30amps.
I cant see that there are any problems with supplying them both with a single 4mm on 32mcb, (installation method c)
i have normally supplied it in 6mm but just wondering really. is it just bad practice, in case they uprate the ovens?
 
If they update the ovens then they need to uprate the mcb too..
If your calcs are all ok then stick to 4mm

Must be short runs though, with no insulation, etc?
 
Last edited:
I am often installing two 3.5kw ovens in one kitchen which amounts to 30amps.
I cant see that there are any problems with supplying them both with a single 4mm on 32mcb, (installation method c)
i have normally supplied it in 6mm but just wondering really. is it just bad practice, in case they uprate the ovens?
Will depend on what the cable sizing calculations turn up, doesn't it???????????
 
Much prefer 4mm for terminating in tight spaces , single boxes etc...so much neater and easier to fold back in.
 
So bizarre when you run a 6mm then from the cooker outlet plate you use their cable that is a 1.5 or 2.5mm flex - I sometimes shake my fist at technological improvements!
I’m deffo one for 4mm runs if cable length and load don’t scupper the idea.
More people are having duel fuel so it’s a piddly oven that will never get over 9 amps with the wind behind it!
 
Good thread, I've had this discussion before. Simply put do the calcs on the cable / installation method and fit the right cable - if that's 4mm then so be it. However, a look at the manufacturers data sheet will advise the size they recommend (this has little regard to the installation method of course)! I do wonder how many ovens were fitted (with installation calcs) and then loft / void was filled with insulation maybe years later negating the installation!
 
Remember - if the oven is delivered and fitted by the supplier, they will simply not install it if they deem the cable the wrong size and they are told the 'minimum' size it should be. Your calcs may be correct but the oven / hob doesn't get fitted and you get called back - not good.
 
I'd run 6mm.

When the electric ovens are replaced with new fangled Fusion energy ovens, the cooker circuit could be used as an electric charger for one of these

You should always plan for contingencies :)
 
I think that, in this instance, future proofing seems to be a smaller CSA cable - I’m kidding but does seem to be the case!
 
I think that, in this instance, future proofing seems to be a smaller CSA cable - I’m kidding but does seem to be the case!

Interesting! Reading recently that as we move to more energy efficiency the csa will go UP so the cables run cooler for such loads. I think we'll see the regs pushing more for this in the 19th... 20th? I wonder how much influence the cable manufacturers have on the IET?
 
use 1.5mm strung in free air. dry the dishcloths on it. 2 uses for the price of 1.
 
I have seen many a kitchen fitter using 2.5mm cable and spur off the kitchen ring . This is used for a cooker and hob, absolutely shocking and when I ask I get the attitude , just wait till Xmas when they have the oven on and all the rings maybe even the grill , if I'm right they won't be cooking any Xmas dinner as that cable will be melting ( am I right )
 
I am often installing two 3.5kw ovens in one kitchen which amounts to 30amps.
I cant see that there are any problems with supplying them both with a single 4mm on 32mcb, (installation method c)
i have normally supplied it in 6mm but just wondering really. is it just bad practice, in case they uprate the ovens?
Though 4mm2 can be acceptable, I would prefer to use 6mm2.
As you say they may uprate the ovens.
Then again, I have no idea in the difference in price between 4mm2 and 6mm2.
 

Reply to oven supplies 4mm or 6mm??? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock