Hi all please could someone help, my ovens keep tripping the rcd see images for details basically from the cu I have 63 amp rcd with a 32 amp mcb type b from that run in 6mm t&e to an isolation switch 50 amp then more 6mm cable to a dual cooker outlet then 2x flex runs to 2x single ovens 2100w each oven power everything up all OK but then put both on full power just as I would when cooking and it trips the rcd going out of my mind as I just can't think why can anyone shed light onto this please Oven wiring help please keeps tripping IMG_20211023_052837 - EletriciansForums.net
 
If the RCD is tripping then there is almost certainly a fault somewhere downstream of the RCD. It's unlikely you'll find it by trial and error, so I recommend you get an electrician competent in fault finding to look at it.
 
As above , you're going to need an electrician regardless

Probably downstream ,one of the ovens faulty

Or even the oven total loading tripping an N-E fault on the rcd ?
 
Is this a new installation?
Or was it O.K before and has recently started tripping?

If new it can be a / both faulty oven elements, if old ovens it can be faulty elements.

As above have you tried each oven singly?

It may be that each oven, whether new or old has earth leakage on the oven element, not enough to trip the RCD, but the combined leagage is enough to trip.

Presumably you've checked all the connections for tightness?
Is there a cable trapped somewhere or nail or screw through one or both?
 
Newb here so don't laugh if this is a stupid suggestion, but isn't it pointless having a 50a breaker after a 32a breaker? Or is the 50a just an isolator that is rated at 50a?
 
I would begin by testing the circuit, with the ovens disconnected, and the L and N disconnected from the consumer unit.
As a retired electrician, do you still have an insulation resistance test instrument?

If the circuit wiring checks out ok, then I might subject the ovens to an appliance tester. And/or use my earth leakage clamp meter on the L and N of the RCD.
In other words, a logical step by step approach usually works best.
 
If they are brand new ovens, not been used before, the elements may have absorbed moisture in storage, and the combined leakage can trip the rcd. Once they dry out they'll be fine.
(this is a known effect - I'm not making this up!)
If one oven will stay on, you could try running one and then the other for a while, and check the effect goes away.

The more satisfactory course of action is to measure the earth leakage current.
 
Last edited:

Reply to Oven wiring help please keeps tripping in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock