Evening all...just a quick question. A customer was using a wallpaper stripper on a ring circuit, smoke started coming out of the back of the socket before the 32amp breaker tripped, what I don't understand is why the 13amp fuse in the plug didn't break? Could someone tell me why? Thanks
 
faulty socket or dodgy connection at the back of the socket, wires got heated, insulation melted and current sufficient to trip 32A went in.
 
Loose connection either in the plug, or at the socket outlet.

Possibly a too-small conductor for the steamer, though unlikely.
 
Steam cools,water acumalates behind socket,tracking between L+N or E ( no rcd) breaker current exceeded and out it goes
Plug top fuse intact because there is no excess current after the socket terminals
 
Fuses dont operate as fast as MCB's.
Now I dont have a BGB to see how fast a 32A MCB operates and at what current but Apparently a 13A Fuse is required to operate at 1.9 times rated current (24.7A) within 30 minutes.
So if its operating at say 40A it may take 15mins to blow where a MCB will probably operate faster.

Did you find what caused the fault?
 
Ive see temperatures in switch gear weld the terminals and cables yet the heat damaged HRC fuses don't operate..... the current needed to operate the fuse-wire needs to get it white hot, so in principle heat generated by a loose connection may not get anywhere near the same temp that is needed to melt the fuse wire.... when you've seen fuses glowing red without operating its an headscratcher the first time ....same principle applies with plug-top fuses.
 
Not sure what caused the fault, going to put it down to either water getting into the back of the socket or a fault in the wall paper stripper, tested the circuit and found nothing wrong.
 
If its any consolation, i went to a tripped 32A socket MCB which was caused by a coiled up extension reel feeding a 2KW heater. THE 10AMP fuse on the reel plug head was still going strong.......

Pffttt thats nothing!
We had a fire alarm go off caused by 2x 3kw heaters plugged into a 25m rolled up lead.

It was a pile of PVC mush and coper when i got to it LOL
 
I remember a few years back and one of the in ln laws wanted to borrow my welder,I asked him if he wanted the extension lead as well,because I had a nice heavy one for the welder.No he already had a nice new lead,anyway he brought the welder back later very annoyed as it had "broken" his new lead! He had bought one of those 50 foot roll ones from one of the sheds,pulled off about 20' and started to weld,his welding on the metal wasn't that good but he'd made a lovely job of "welding"the cable to the reel.obviously he didn't see the bit about unwind fully before use.
 
Also don't forget a fault will usually take the weakest part of the circuit out. i.e if your ring main is already running at 25A with 7A to spare. 7<13 so you will probably take the MCB first. Well so I have always been led to belive.
 

Reply to Overcurrent in circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am using a 160watt-200watt multi uv tube stand alone sunbed,When the 2 power leads (plugs protected by 2x13amp fuses) plugged into a double wall...
Replies
9
Views
721
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
709
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
793
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
256

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock