Going to a garage tommorrow were they have just had new LED lights installed.
After a while the photocell overload breaker trips, the photocell is connected to a contacter the RCD protecting the whole circuit never trips.
The light units that have been installed are approx 1/3 of the wattage of the previous lights.
No previous fault regarding tripping have been reported.
The new lights go through a earth leakage test and IR test before they leave production.
Any1 have an idea what it could be?
 
Going to a garage tommorrow were they have just had new LED lights installed.
After a while the photocell overload breaker trips, the photocell is connected to a contacter the RCD protecting the whole circuit never trips.
The light units that have been installed are approx 1/3 of the wattage of the previous lights.
No previous fault regarding tripping have been reported.
The new lights go through a earth leakage test and IR test before they leave production.
Any1 have an idea what it could be?

Should !! , probably a fault in the photo cell or the contactor coil is duff check for water ingress at the fitting to , would be better if we had some more info to mcb to lighting circuit via contactor and RCD or is the photo cell off its own mcb supplying the contactor coil etc
 
Not been on site yet, so details of mcb's and which circuits are fed from where are unknown but the photocell has its own apparently - owner tells me!!
What install reason could cause the breaker to trip but not the RCD to trip - confusing as when they reset breaker all is fine for an hour or so then it trips again!
 
sound to me like a shorting problem , this may not cause the RCD to trip ,think about your RCD as a set of scales its perfectly balanced if the balance is offset the RCD will trip some times a short may just trip the MCB and not the RCD , or if the RCD is faulty it will not trip either first thing i would do is check the function of the RCD then check the fitting connections and also see if there is water in the joints for the lights if the RCD is faulty then the joints could arch away if its got water in and the RCD wont trip , its test kit out time im affraid
 

Reply to Overload breaker tripping. in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock