i have just moved into a 4 bed house with a 100amp main isolator in the consumer unit, PME supply with mcbs. The house has 2 showers of 8.5 kw each, electric oven 2.3kw, immersion heater (assumed to be 3.0kw), 3 lighting circuits, plus 3 ring mains for 13 amp sockets. Even after allowing for diversity is not the main isolator switch overloaded? It is quite possible that the oven and both showers could all be on at the same time (i.e. 84 amps), if the immersion was on as well this would be 97 amps, leaving only 3 amps for other things like kettle, tvs(x3), freezers(x2), lights, etc. One side of board has RCD , but no RCD protection to the showers (!), only to the 3 ring mains. Opinions and advice please.
 
The oven and immersion will have thermostats so will cycle on and off. The showers will only be on for relatively short periods of time so I think you'll be alright. If you're worried, perhaps you could set the immersion to come on at times the showers are not likely to be used?

I would definitely get the lack of RCD protection on the showers sorted out though!
 
As mentioned, the lack of RCDs for the showers is a priority.

The service fuse on the incoming supply will be a maximum of 100A, and it might well have a lower value fitted, e.g. 80A. It will withstand a significant overload for the time it takes some to have a shower (well, perhaps my daughter excepted).
 
Why not clamp (or get somebody to clamp) your meter live tail so that you can see what the actual demand is when you turn everything on. It is usually significantly less than you expect.

You can also get energy monitors quite cheaply which display your energy usage in real time, I came accross an 'owl' one Friday.
 
Quite the informative video on max demand / possible overload


Some interesting opinions that chap has ...... about 15 mins in a reference to non compliance of 314 for more than 1 cable in an mcb ........ hope he didn’t C2 that

On a reality level there are so many installs like this around ....... be interesting to see what happened next !
 

Reply to Overloaded consumer unit ? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock