Hi, just wondering why there would be 179V at a light box from the home run to ground. At the panel the breaker reads 118V to ground. what's the reason for such a large spike?
This circuit has also malfunctioned recently, causing the investigation.

Thanks,
Sylvia
 
Hi, just wondering why there would be 179V at a light box from the home run to ground. At the panel the breaker reads 118V to ground. what's the reason for such a large spike?
This circuit has also malfunctioned recently, causing the investigation.

Thanks,
Sylvia
Sylvia welcome to the forum your problem is outside in your service. The # 6 bare wire which has come loose or the power company has problems. Any time I’ve ever read 180vac on any outlet I know for sure you have a problem with continuity from the power company’s wire coming to your meter to the actual ground rod. Please call an electrician and let him read this. This could cause a fire, you have 120vac and it’s all good but 179vac can fry your tv, microwave, clocks any thing plugged into a duplex receptacle I promise you your problem is at your service Good luck
 
You have an open neutral in your circuit! Check all junction box neutral wire splices leading up to the light. The reason your light box is reading 180V is because your circuit has now become a 240V series circuit caused by the open neutral. Your other loads on the circuit are now receiving 60V.
 
You have an open neutral in your circuit! Check all junction box neutral wire splices leading up to the light. The reason your light box is reading 180V is because your circuit has now become a 240V series circuit caused by the open neutral. Your other loads on the circuit are now receiving 60V.
Zeuss88 they have an open neutral problem but I still say it’s at the service.
 

Reply to Overvoltage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
653
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi I have a 3phase shop in a high humidity area in (Hawaii) and I'm having some issues with low voltage on the single phase outlets on the 120v...
Replies
6
Views
859
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
371
I have a Single Phase Power box for a townhouse. When I read voltage across the Hot legs (A) and (B) to ground I get 123 volts with the main...
Replies
1
Views
917

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock