Discuss Parallel feeder cable Question in the Canada area at ElectriciansForums.net
A
ACDC
Hello All.
Not been on here for a while, hoping you guys can help me with this one.
We installed 185mm single copper core aluminium armoureds (2*185mm per line conductor each run 170m) to an MCC feeder. The intend was to use the aluminium armourings as the main CPC.
My question is, how can i work out the CSA of the armouring for the CPC?:confused::confused:
Thanks in advance
There can be issues when using single core cables. Namely circulating currents between sheaths of the cables and eddy currents being generated where they pass through a steel glandplate or enclosure.
See regs 521.5.2 and 523.10
Thanks bomjac, I have installed non-ferrus glandplates in both MCC`s, the customer did suggest a wooden plate...... was a good chuckle for 5mins.
Reply to Parallel feeder cable Question in the Canada area at ElectriciansForums.net
Did an EICR that passed 5 years ago Several things in the picture raised concerns for me. Comments please - photo at end First photo shows a...
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Hello, With regards to Trimble software for bs7671 cable sizing. I understand that a three phase circuit (No neutral) is one circuit and this can...
Hi All, I’m after some advice. I’ll cut to the chase but I can give more detail if needed. A 400A sub main supply needs to be ran 100m, a pretty...