Discuss parallel feeds in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
benji
when testing parallel feeds (say 2x4c70mm) do you have to separately test each cable or test them both connected together as this is the way they will be used
yours benji
I test together. As you say this is how they are used. For peace of mind I also do a continuity check, down each pair, with one set of ends coupled, but that's just me:eek:
yeah as we have about 8 sets of parallel feed upto 185mm we would ground one end to id. each cable but for recordable test readings ie. ins.&cont ect there seems to be mixed feelings whether to test individualy or combined i'm for combined as your loop &psc will be taken when the 2 cables are one,must confess i don't know which is the correct way or what difference it would make
yours benji
I think it's horses for courses a bit and each to their own.
The parallel cables, to me, represent one feed and so are tested accordingly. A site where this was done was used as an assessment review example and received no adverse comments so I guess it's ok.
Anybody else got any thoughts?
Agree with TT. Surely it is the conditions of use that determines the prospective fault currents and the circuit's ultimate performance under fault conditions so that's how any system (electrical or otherwise) should be assessed i.e. in its normal/designed working condition and configuration.
Reply to parallel feeds in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I am installing some driveway lights. The customer wants to be able to switch them on from t he house, but also have a PIR at the driveway...
I needed to illuminate our dark side walk at the house. I have used two PIRs wired in parallel which switch four LED lights. The idea is no matter...
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...