Doing an EICR on a building and a sub board has two 4mm twin and earths feeding it. Cables are connected into same breaker in main db but take different routes to get to sub board. Is there anything in the regs regarding as I cant find anything.

Cheers for any information or advice.
 
Cables should be the same size and the same length, other than that you're probably OK.

523.7
 
Last edited:
As Rockingit stated parallel sub-main feeders need to be of equal size, equal length, and be of the same construction. Ideally they should follow the same route too. There is a very good chance when they don't follow the same route/path, that they won't meet the equal length criteria of parallel supply!!
 
Thanks for the information, just one other question, should I put it down as an observation and what what code would I give it?

If you test the resistance of each leg of the parallel supply, you will know for sure if they are of equal length. I wouldn't mind betting that they are not!! It's your call, if your going to code it without testing though!!
 
As Rockingit stated parallel sub-main feeders need to be of equal size, equal length, and be of the same construction. Ideally they should follow the same route too. There is a very good chance when they don't follow the same route/path, that they won't meet the equal length criteria of parallel supply!!

I have always thought that you are not allowed to have any joints in them as well , but can not remember where i have either heard or read this !?

What would be your thoughts on this Engineer54 ?

Thanks , Dave
 
Joints on a dual 4mm parallel circuit, i wouldn't like to think so!! On substantial parallel supplies, i've seen joints put in direct buried cables, but normally because of damage repairs etc!! Nothing basically wrong with permanent joints in any cable, ...if carried out correctly with an appropriate joint...
 
Thank for your take on it !

I for the life of me can not think where i heard it so maybe i just imagined it ?

It does sort of make sense in a way , but as you say on a professionally made joint it should make no difference .
 
Perhaps your thinking about tap-off joints, on one of the parallel cables, to feed something else?? That's certainly not allowed!! lol!!
 
I have traced both cables from start to finish and there are no joints in them and the outer sheath looks in good condition. Still not sure what code to give it
 
With a difference of 0.05 ohms, the extra length cant be that much. I mean the difference could be down to slight movent of the croc clips when testing. Look in the OSG and do a few calcs and you will see how long each cable is. When you measure end to end on a ring, the L N results can be within 0.05 ohms and still be ok. At worst, going by what you have described, I would say C3 but as others have said its your call. Some wouldnt even code it. I may not code it if I was acctually on site looking at the whole picture.

Jay
 
You can work out the load sharing of the conductors, but a simple clamp meter test should suffice. Assess the load and the supplying PD and make an engineering judgement based on your findings.
 

Reply to Parallel Feeds in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
615
Hi I'm installing two new sub-mains. I need to parallel some of the supply cables. It's the main incomer in 5 x 25mm, with 5 x outgoing 25mm...
Replies
11
Views
2K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
884
Hi. I'm being tasked with installing an electric shower into a property that was built back in the 1980's. The main consumer unit has only 4 ways...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock