• IMPORTANT: Please note that nobody on this forum should be seeking from or providing advice to those who are not competent and / or trained and qualified in their field (local laws permitting). There is a discussion thread on this global industry-wide matter HERE. This also has more information about the warning with regards to sharing electrical advice in some countries. By using this forum you do so in agreement to this.

Discuss Paralleling 8-gauge wires to a 220V Subpanel for Tankless Water Heater in the American Professional Electrical Advice Forum area at ElectriciansForums.net

edwardtx

DIY
Reaction score
0
Hello,

Question is regarding a recently purchased property in Central Texas, which includes a 27KW tankless electric water heater. It is four years old and working fine.

What the prior owner installed is surely not code compliant, but the county does not require permitting for "renovations made within the original square footage of buildings".

The subpanel breakers next to the water heater are essentially nearby cutoff switches. The main panel is 80 feet away.

Aside from the code, is there anything electrically wrong with this setup that it would make good sense to (1) replace the wiring to subpanel or (2) remove the subpanel completely?


Paralleling 8-gauge wires to a 220V Subpanel for Tankless Water Heater 1659636158055 - EletriciansForums.net
t
 

James

-
Mentor
Esteemed
Arms
Supporter
Patron
Reaction score
6,240
I would be looking at removing the sub panel, it looks to be reducing safety rather than improving it.
have you spoken to any local electricians?
 
OP
E

edwardtx

DIY
Reaction score
0
I would be looking at removing the sub panel, it looks to be reducing safety rather than improving it.
have you spoken to any local electricians?
Thanks. I spoke with a couple of experienced electricians in a large electronics manufacturing plant I work at. Neither saw anything "wrong" per se with the setup from a purely electrical circuit point of view. Just looking to see if anyone has a solid argument beyond "doesn't look right"
 

James

-
Mentor
Esteemed
Arms
Supporter
Patron
Reaction score
6,240
The thing wrong is someone could expect that turning off one of the outgoing breakers in the main panel would make the outgoing terminals dead, in this case they would remain live.

in the U.K. if you are running cables in parallel then they need to be fed from the same circuit breaker. (Amongst other requirements)
 

Megawatt

-
Esteemed
Arms
Reaction score
1,416
B
Hello,

Question is regarding a recently purchased property in Central Texas, which includes a 27KW tankless electric water heater. It is four years old and working fine.

What the prior owner installed is surely not code compliant, but the county does not require permitting for "renovations made within the original square footage of buildings".

The subpanel breakers next to the water heater are essentially nearby cutoff switches. The main panel is 80 feet away.

Aside from the code, is there anything electrically wrong with this setup that it would make good sense to (1) replace the wiring to subpanel or (2) remove the subpanel completely?


View attachment 100096
t
By Code you are not allowed to parallel nothing under 1/0 wire, and that’s a big tankless water heater. You wire size needs to be # 3 at a minimum. My mission is to tell you the correct answer to your question by code. You live where you live and if code enforcement doesn’t care then all I can say is good luck with your project
 

Reply to Paralleling 8-gauge wires to a 220V Subpanel for Tankless Water Heater in the American Professional Electrical Advice Forum area at ElectriciansForums.net