First time post although avid reader. And first post is a question, sorry!
What are people's thoughts about paralleling fuse boards. Been asked to install a new board by linking off the existing boards supply as the current board is full. They are lug and bolt terminals so can easily double the cables up and the existing cable and supply breaker from the LV panel is big enough to protect both boards. Apart from the obvious problem of both boards going down should a fault occur on the cable, which the client understands, is there any reason why this can't be done.
*Puts tin hat on.
 
Il say nothing wrong if can take booth cables... But I'd come from underside.. So when isolate one the both isolated . Or as above use iscos..
 
You could make yourself a spare way in existing board by extending a circuit into the new board. Then use the newly created spare way to supply the new board.
 
Take a circuit from old db, assumed 3phase, to new db to clear a space for a new breaker.
Fit 63a tp breaker in old db to feed new adj. db.
Then old db isolator kills both as E54.
All depending on loads of course.
Maybe move the circuits around to feed the lighter loads from the new db?

Boydy
 
That's what I said :)
 
if you have a full board, and want more circuits, then either fit a bigger board or split the tails.

As long as there is sufficient upstream protection, then there shouldn't be a problem.

If upstream protection is a problem, and only IF, then this is when you need to add another (board off a board) if you see what I mean!

If the upstream fuse will cope with the extra demand, then there is no need to add more protection, just treat it as a bigger board and do as I said.

Basically, you are only increasing the capacity of a small board (within the capacity of the supply cable).
 
As E54 pointed out, you need a common point of isolation. I don’t like the method but done correctly, there should be no problem.

A single isolator cabinet mounted midway under the two boards serves the purpose.

This is all dependant on the possible load increase and diversity.
 
Thanks for your replies

Its a 630a 3 phase supply using 300mm singles. The existing board is full as I say but pulling around 80-90a per phase. The board has a 400a disconnector built in. The new board will be the same as the existing. Client not really keen to remove cables and split in an isolator or sub panel as this will cost a lot more and increase down time.

Can someone point me towards the single point of isolation
regulation please as I'd like to look at that in more detail. I've seen reg 537.1.3 which says each installation needs provision for disconnection for supply.
So if that applied then maybe the 630a MCCB could be classed as isolation for both. Obviously suitably labelled.
 
Thanks for your replies



Can someone point me towards the single point of isolation
regulation please as I'd like to look at that in more detail. I've seen reg 537.1.3 which says each installation needs provision for disconnection for supply.
So if that applied then maybe the 630a MCCB could be classed as isolation for both. Obviously suitably labelled.

I was thinking the same. Common points of isolation are very rare in large installations, unless fire service has requested a building isolation point. It is quite possible to have multiple supplies onto a bus bar that goes out to multiple distribution boards. If you have a single incommer from the DNO this would normally be your common point of isolation. What is upstream of these 300mmcables?
As an observation most domestic installations with a PV system do not have a common point of isolation.
 
Could you not get an extension board to sit on top of the existing one ?
most of the ones I've come across do a link kit of some sort
 

Reply to paralleling fuse boards in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
257
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi Doing my first Inverter and Battery install on a domestic property having just completed my EESS course with LCL. Question is how do I...
Replies
17
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock