Hello, can you parallel conductors to reduce Voltage drop? Got a job were voltage drop is an issue and I can't upgrade cables because of cost. Will paralleling conductors of same csa double the csa and reduce voltage drop, and is it allowed in regs?
 
Read up on Appendix 10.
To keep things simple, cables should be the same type, CSA and length, don't forget to check the tables in Appendix 4 for derating factor based on installation method.
 
Thanks lads thought it was ok, just wanted it confirmed.
The cabling runs from supply to three d/bs first two are 3phase boards and third is a single phase. Will it be ok to increase the csa on L1 of 3 phase cable between d/b 1 and 2 then increasing single phase csa to d/b 3.
Basically is there any issue having one core on a three phase supply with a larger csa?
 
Out of interest, where is the extra core you are doubling up for the L1 phase coming from? A core currently used for Earth in the same cable (if this is SWA)?
 
You can't just increase the CSA of one of the phase conductors of a 3-phase supply, you must also uprate the neutral and earth accordingly. It's also going to get tricky with OCPD's as well...
 
Hi lads thanks for replys. Did think the paralleling of L1 could be a bad idea don't want to risk damaging any equipment.
Have to talk with customer again, only option is cable upgrade.
 
If the cables are being paralleled only to keep VD on the most heavily loaded phase within specs, rather than to provide adequate CCC, then there will be no harm electrically. However, you will have a very non-standard circuit configuration that might be difficult to explain on the cert, and things might go wrong if it is modified in the future.

Personally, if I had excessive drop on one phase due to unbalanced load, and a spare core, I'd parallel it with the neutral. A stiffer neutral is always better, and it will do as much to reduce the VD of the unbalanced part of the load as paralleling it with the line. In some applications that generate heavy 3rd harmonic distortion, the neutral has to be larger than the lines anyway.

Do you have any figures to give an idea of how far things are adrift with the existing cable?
 
How many circuits on the single phase board? Could they be split and have that DB as a three phase to help with balancing?
 

Reply to Paralleling to reduce Voltage drop in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
507
Hi, This relates to our planned PV installation. The G99 application came back outside SSEN's limit for voltage rise, which for property connected...
Replies
10
Views
2K
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
910
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock