markadams

Regular EF Member
One of the questions on a recent Part P assessment was how would I wire an external outbuilding if the earthing arrangement to the property was PME.

I said I would run a three core SWA from the property to the outbuilding and use the cable armour and the third core as the exported CPC.

I was highly criticised and was told that I should install a rod at the property and at the outbuilding.

I can find no mention of this in 17th ed AMD3 book, can anyone tell me where i would find this if it is the case.

I have had a couple of other Assessments previously where they have checked out building installs and never mentioned this so I am not happy.
 

westward10

In echoed steps I walk across an empty dream.
Staff member
Moderator
Should have asked where this is stated in black and white.
 
  • Like
Reactions: DPG

markadams

Regular EF Member
Stroma, I am at the moment but I just wanted to check my facts as the assessor was insisting that I was wrong and listed it as a non-conformity.
 

westward10

In echoed steps I walk across an empty dream.
Staff member
Moderator
If he is going to list it as a non conformity he should show you evidence.
 

kenny7askew

Regular EF Member
seems a bit odd/harsh to give a non compliance for the answer you gave to a verbal question
without the opportunity to look it up
 

telectrix

Scouser and Proud of It
Respected Member
the assessor is wrong. you would normally only need to make the outbuilding TT if it was a metal structure or if the 3rd core of your SWA was inadequate for bonding purposes (min. 10mm for PME ).
 

westward10

In echoed steps I walk across an empty dream.
Staff member
Moderator
I assume this outbuilding was nothing out of the ordinary.
 

mattg4321

Electrician's Arms
I've been hearing through the grapevine that Stroma are starting to become extremely harsh with their assessments. On the face of it this should worry us less than the other extreme, but some of the reasons for non conformances do make you wonder whether they do it to make you pay for a re-visit.

I've heard this through my Elecsa assessor recently (so he ma ybe biased), but also through a friend who is registered through Stroma. He received a non conformance due to fixing sockets inside kitchen cabinets. The assessor claimed accessories had to be fixed to the fabric of the building and not kitchen furniture. Complete garbage as we all know. I forget whether he had to have a re-visit or not.
 
  • Like
Reactions: DPG

Wes1000

Regular EF Member
In the IET guide to the building regs 5.7.3 states making the outbuilding a TT as an alternative method to how you suggest.
 

Electrician Talk

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Electrical 2 Go - Electrical Supplier and Electrical Wholesalers
Electrical Insurance
ElectriciansForums.net (formerly known as ElectriciansForums.co.uk) was setup in April 2006 to provide free electrical advice to both professional and DIY electricians. Whether seeking advice for auto electrics, trying to find electrical installation condition reports (EICR) form downloads, or whether you're here just to talk to other electricians; we've been a first-choice website for tens of thousands of sparkies for well over a decade.